ge 90-30 logixmaster, cimplicity

cdyer

Member
Join Date
Apr 2013
Location
searcy arkansas
Posts
5
got a huge problem with a 90-30 on a stator welder we got from a mexico company. we do not use GE plc's in our plant it is all allen Bradley for us. the problem we have is the quickpanel jr is saying , no comm with plc. we have a copy of the logixmaster software, but from what can can figure out is that one possible program was wrote in versapro software and the other was cimplicity. so my question is that if the program was made using versapro or cimplicity the logixmaster software we have will not do us any good?
 
Correct. The GE products are upgradable, but not downgradable. If you use a newer version, you must keep using that version, or a higher one.

Proficy is your best bet at this point. Pricy for one device, though. A contractor (or a good friend!) is a safe bet for one time troubleshooting. Otherwise, Proficy will do it. It's huge advantage is being able to do PLC and HMI using the same points, in the same program. I like it a lot for that reason alone.

Once you get it, load the PLC, then the HMI program into Proficy/Cimplicity. Once you save the project, you will be up to date. Chances are you will have to download to the PLC and probably the HMI once the import is done. Then the correct flags will be set letting you go online.
 

Similar Topics

Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
158
Hello everyone! This is my first time posting, though I have been to this site a few times hunting for some random problem like we all do. I...
Replies
4
Views
173
Hi good day Everyone, I have a cimplicity v10 project with 7 to 8k tags communicating with AB PLC through OPC and Rslinx classic. I have this...
Replies
3
Views
217
Hi All, I am trying to program some new Versamax micro PLCs through PAC using some programs saved in our archive however whenever i go to import...
Replies
2
Views
123
Hi All, Im using Cimplicity 8.2. after the last restart Server Scada, the PTDL_RP process can not running. so Process can not be login to database...
Replies
2
Views
158
Back
Top Bottom