[FONT="]I am trying to communicate data between a Miri AD2006 and an Omron CP1H using the Modbus protocol with the Omron as the Master ( We can’t find documentation or settings that indicates it can be a slave). We are using RS485 2 wire connection between the units. I have programmed the Omron using it’s “Easy Modbus-RTU Master” setting’s and it appears as if it is doing the right thing. It is sending data out of communication port 2 on the RS485 network as indicated by it’s lights, but it is returning a fault code 80 which is “Response Time out, A response was not received from the Servo”. This indicates to me the Miri is failing to recognize the signal that it has received. If anyone there has had any experience with this it would be greatly appreciated if you could pass on any information.
[/FONT] Miri
Type: AD 2006
Identifier: 14
Port 3: RS485, No Polling, 38.4k, N, 8, 1,
Protocol Options:
Data Type = RTU
PLC Address 1
Omron
Type: CP1HXA
Serial Port 2: Mode = Serial Gateway, 38400, 8, 1, N,
Response Time out 250ms
Easy Modbus RTU Master Memory map / command Block information
Fuction destcription
Address
Value Hex
Modbus Slave Address (bits 0-7)
D32300
#0001
Modbus Function Code (bits 0-7)
D32301
#0010
Number of Comm Data bytes
D32302
#0007
Modbus slave register address
D32303
#9c41
Number of Modbus slave registers to write
D32304
#0001
Number of Modbus slave data bytes (bits 8-15)
D32305
#0200
Data to send (D32306 upto D32349)
D32306
#700B
Modbus Error Code
D32352
#0080
Easy Modbus Execute Bit
A640.00
(1 when executing)
Any help would be appreciated
[/FONT] Miri
Type: AD 2006
Identifier: 14
Port 3: RS485, No Polling, 38.4k, N, 8, 1,
Protocol Options:
Data Type = RTU
PLC Address 1
Omron
Type: CP1HXA
Serial Port 2: Mode = Serial Gateway, 38400, 8, 1, N,
Response Time out 250ms
Easy Modbus RTU Master Memory map / command Block information
Fuction destcription
Address
Value Hex
Modbus Slave Address (bits 0-7)
D32300
#0001
Modbus Function Code (bits 0-7)
D32301
#0010
Number of Comm Data bytes
D32302
#0007
Modbus slave register address
D32303
#9c41
Number of Modbus slave registers to write
D32304
#0001
Number of Modbus slave data bytes (bits 8-15)
D32305
#0200
Data to send (D32306 upto D32349)
D32306
#700B
Modbus Error Code
D32352
#0080
Easy Modbus Execute Bit
A640.00
(1 when executing)
Any help would be appreciated