Profibus network using AWG#20 Shielded twisted pair

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Dear Automation experts,
I want to use the existing lonworks network which uses AWG#20 Shielded twisted pair for my Profibus system because I find difficulty in setting up a new Profibus cabling. This shielded twisted pair lonworks networks are properly installed in a 1/2 inch metal piping.

My question is can I use this without any issues?
Need your advise on my plans.

Thanks,
APS
 
You cant just exchange one type of shielded cable for another when using it with diverse bus networks.
It may work ok, or maybe not. Noone can give you a reassurance that it will work.

If you Profibus speed is 19.6k or 187.5k then maybe it will work.
If you Profibus speed is 1.5M then probably it will NOT work.
If you Profibus speed is 12M then certainly it will NOT work.
 
Profibus cable specification

Hi
Just check out specification of profibus cable over here. Reproduced here for ease of reference
Cable specifications: What should I use?

The PROFIBUS standard defines two variations of the bus cable. However it is recommended to use cable Type A in all new installations.

Type A is recommended for high transmission speeds and permits a doubling of the network distance in comparison to Type B.

Type A Technical specification:

Impedance: 35 up to 165 Ohm at frequencies from 3 to 20 Mhz.
Cable capacity: < 30 pF per meter.
Core diameter: > 0,34 mm², corresponds to AWG 22.
Cable type: twisted pair cable. 1x2 or 2x2 or 1x4 lines.
Resistance: < 110 Ohm per km.
Signal attenuation: max. 9 dB over total length of line section.
Shielding: CU shielding braid or shielding braid and shielding foil.
Max. Bus length: 200 m at 1500 kbit/s, up to 1,2 km at 93,75 kbit/s. Extendable by repeaters.

You have to see if your cable matches above specs, if not then behavior cant be foretold. Just as a side note what I have seen is that if there are sharp bends then signal (voltage) drop is high.

Regards
Manmeet
 
Or just paint the shield "purple", that should do it.


Even if it meets those specs, remember if it is not purple (Profibus certified), it will not be supported by any of your device manufactures, so if you have a problem you will be on your own.
 
You may know what you did but think of the poor basta*d that has to come behind you and figure this out at 2:00 am 10 years down the road. Just get the correct cable and do it right the first time.Taking shortcuts like this will always come back to bite you in the arse.

As my grandpa always told me. "If you can't do it right just don't do it at all"

Rant Off.
 

Similar Topics

Hi, I have a doubt about the system architecture shows below: could two master devices install in same profibus network?
Replies
4
Views
2,643
My Siemens Step 7 education progressed today. I'm getting more familiar with how it all works, but at the end of the day I got stuck trying to...
Replies
0
Views
1,016
Hi, I'm retrofitting an Anybus-X Gateway as a Profibus Master on an existing Profibus segment. I'm wondering if this needs to be the last device...
Replies
3
Views
1,211
Dear Superiors,📚:wizard: I'm new for s7-300 and yaskawa v1000 drives communication via profibus. My aim is to find how to run the drive or...
Replies
1
Views
1,739
Good day, I have a problem regarding the configuration and commissioning of a profibus network where the master will be an S7-1500 PLC and several...
Replies
3
Views
1,797
Back
Top Bottom