RSLOGIX 5000 PID Tuning Parameters and Thermal PID Loop Tuning
msohaibbutt
Apr 2015
PK
I am using PID instruction in RS Logix 5000 with independent equation. I am confused about its tuning. Please somebody explain under listed queries:
1) How increasing/decreasing tuning parameters will affect the controller action.
2) If i do not use Integral and derivative parameters how it will affect the controller action.
3) RSLOGIX 5000 instruction manual mentions SP-PV as direct and PV-SP as reverse but for a reverse acting PID loop when i chose SP-PV then my controller was acting as reverse. Why is that?
4) I have a thermal loop which i need to tune. I am only using KP=8 while rest of two are zero. When the controller increase the output to attain setpoint, PV overshoots because of slow rise in temperature. Same happens when the temperature is decreased. How should i tune the controller to solve this problem?
Do a google search for Zeigler Nichols. Follow the instructions. Or do a search for the many threads in here that answer the same question.
Some tips: Use the PIDE block instead of PID. Try the autotune feature. Be warned, though, PID tuning can take patience and a lot of experience. Temperature loops can have a lot of deadtime and the autotune often stops way too early to give appropriate gains. Good luck.
Hi, Long time not in the forum, and not in the programming. I´m getting back. I was issued a conversion from RSLogix 500 to RSLogix 5000 (studio...
1,289
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
894
Hi All, I have a PID control application that I would like to get your opinions on. As I am reality new to PID loops I am struggling somewhat...
4,279
Hi, I am confuse with the scaling tab on the PID dialog box. On the Process variable I am using a tag that is already scale. 0 to 16 Feet Level...
2,420
Hi I am trying to understand the best method of providing bumpless transfer to the PID function (not PIDE) The existing code shows In Manual...
4,615