Me and my coworkers have been troubleshooting a starter failure for a Cutler Hammer Soft Starter for a 100hp motor. The motor when put in either Hand or Auto will start and after 2 seconds a timer instruction in the PLC will cause a Starter failure. The motor has just enough time to get past its inrush current before it causes the starter failure. In the PLC if it does not see a Starter Energize Bit it will cause the timer to time out and cause a failure alarm. We have megged the motor leads and windings, test was good. All fuses are good. This is a brand new starter, it was replaced 3 days ago because the old starter's contacts were very badly pitted. This is one of 2 motors that are supposed to work simultaneously and there is a 5 second delay as not to cause a large surge on the generator. They are pipeline pump motors that were upgraded from 60hp because of the load. I hope this is enough information about the situation. Any suggestions would be helpful, thanks.