I installed a new ABB FEX 300 flowmeter which after a test run for a while it started giving errorneous reading.
It is now indicating a false zero reading(0 L/H) on its display when the pump is running.
What could be the issue?


Kind regards,
D.KAMAU.
 
Since they stopped making the MagMaster, ABB haven't made a new flowmeter that wasn't ****. So that's your first problem...

Is it metal pipe? If not, do you have grounding rings installed?

Is the sensor body bonded to the transmitter with a low resistance earth?

Did you terminate the sensor cabling correctly? If you shortened the factory supplied cable, did you remove the sheath from the screened electrode wires properly?

What is the process liquid?

Is the meter full pipe? No trapped air?

There is a diagnostics menu... does it indicate any faults?
 

Similar Topics

hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
Replies
0
Views
41
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
228
I have to start out by saying I am not a PLC programmer and I have basic programming skills but mainly use software as a troubleshooting tool. I...
Replies
0
Views
120
Does anyone have an example project of the cm ptp ET200 SP HA with 410-5H DCS (PCs7 9.1 SP1) for MODBUS MASTER/SLAVE communication ?
Replies
2
Views
121
I want to buy this program if anyone has it. Absolutely no one has it officially for sale. My cpu is IC610CPU104B My mail...
Replies
2
Views
104
Back
Top Bottom