SLC 505 to PV+1250 via e-net

lifetech

Member
Join Date
Dec 2012
Location
Arcade, NY
Posts
39
Hi again
my latest crisis is this: one of the slc 505 processors on a network failed yesterday. I took a used processor (the only one we have) off our shelf and loaded it and now were back up and running... except the rs232 port on this processor does not work and there needs to be pv+ in this port on dh485.
Untill I can get a new 505 in, I would like to put the PV+ on e-net and communicate with the 505 on that platform.
My problem is that in rslinx enterprise, this processor does not show up in design or runtime, therefore I cannot direct my short cut to the required processor. I attempted this online and rs linx sees the entire network, and also the comms tab in explorer see the entire network.
How can I add this processor to the local and target positions so my shortcut points to it?
Thanks!
 
From release 1993-1999, the SLC-5/05 only supported the older A-B proprietary Ethernet protocol, called "CSPv4". The EtherNet/IP protocol (shared with the MicroLogix and ControlLogix) was added after the ControlLogix came out.

RSLinx Enterprise, and therefore the PanelView Plus terminal, does not support the old CSPv4 protocol.


The embedded web page of the controller should tell you the firmware revision (as will RSLogix 500). We could look it up from that.

An unambiguous way to determine if the controller supports the old and new protocols is to use a command-line tool called TCPING.

TCPING 192.168.1.xxx 2222 will succeed on both old and new controllers.

TCPING 192.168.1.xxx 44818 will succeed only on new controllers.
 
Right you are again, Ken. This is an old controller. I think I will wait untill the new controller comes in, then put it on e-net.

Thanks for your help!
 

Similar Topics

Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
57
Hello, I inherited a control system one of my predecessors thought it was a good idea to put logic for cant optimization and Kinetix motion...
Replies
15
Views
3,526
Probably a silly question and asked a hundred times already, but i tried to do some searching here and couldn't find this question. I have 502's...
Replies
9
Views
2,970
I'm a mega noobie when it comes to PLCs and the such. I'm a network guy. We are currently experiencing an issue where the SLC immediately faults...
Replies
8
Views
1,875
Hi guys I hope your all safe and well , I have a question regarding a slc 505 on ethernet is it possible to add a ethernet remote I/O module...
Replies
5
Views
1,859
Back
Top Bottom