ML 1400 & 1762-OF4 Operation
Is the 1762-OF8 configured for "Raw Proportional"?
If so a "MOV" instruction is all you need
Source N7:4 (value 31176 = 20ma)
Destination O:2.0
A "MOV" instruction is all you need for the 1762-OF4 also
Source N7:4 ( value 31206 = 20ma
Destination O:2.0
Mickey, I used your MOV instruction suggestion. The less math calculations the better for faster execution. Please see attached screenshot. The first MOV, moves the selected speed to N7:4, the second moves the N7:4's value to 1762sc-OF8 module (did not work) and the last MOV instruction moves the value to 1762-OF4 module, which worked perfectly.
What could be wrong for module OF8 module? the module now shows a blinking indicator LED. Before including the OF8 MOV instruction it was a steady indicator LED, meaning it was fine.
I have not used the 1762sc-OF8.
But per the manual the raw values are different then the 1762-OF4.
Are you sure the 1762sc-OF8 is configured for "Raw Proportional"?
Hi I need to wire module 1762-OB16 (DC Source Output Module). The module is connected to my ML 1400 PLC. I am a bit confused with the wiring, on...
1,656
Hi all, I have a Micrologix 1400 BWAA and the correct software for it. I would like to learn to program PWM to control a stepper. I am currently...
2,596
Dear Sirs, i have a problem with my micrologix 1400 with analog input 1762 if4 . I have set the hardware jumper for Volt and i added the...
2,689
Hi Need help. I'm new to the plc progamming specifically Allen Bradley PLC. I am planning to create a control for an oven. using Micrologix PLC...
2,510
We have an application using a ML1400 with five 1762 I/O modules attached. We've run out of space in the panel and would like to locate some I/O...
5,085