Rs485 Modbus RTU Master

Join Date
Dec 2013
Location
New Damietta city
Posts
34
Dear experts,
In my project, I am establishing Rs485 Modbus Rtu Network.
My problem that the master located in between of slaves.
So, Can I put the Modbus Master in between of different modbus slaves not in the start or end of network??
Thanks.
 
Yes.

Some masters have built in end of line terminating resistors. Make sure these aren't enabled.

Make sure you have terminating resistors either end of your network.
 