SLC 504 to ControlLogix MSG on DH+

The data table format of PLC-5 and SLC500 Integer "N" files are 16-bit "INT"


The default integer data format on ControlLogix is 32 bit "DINT". Is your message data arrays in your ControlLogix configured as a data type of "INT"?
 
Last edited: