Hi to all ,
I don't have a good experience in PLC ( you can say a beginner )
I had a problem with a PLC S5 135U /155U CPU 928B
The problem is i can't understand a network where it's written in STL and CSF
The Flag is F 15.2 and it's related to stopping the machine ( F15.2 is on randomly when the machine is running or stopped ) and the only way to run it back is to reset PLC
here is a picture of the PLC when it's Running or ready to run
and when it's stopped
Hello
IF one or more bits in FW124 OR FW126 OR FW128 are ON OR Input 18.1=OFF OR input 6.4=OFF then F15.2 goes to ON state.
In your screenshot FW124 = 8 so not equal to zere and thats why F15.2 goes to ON state.
FW124 HEX = 0 0 0 8
FW124 binary = 0000 0000 0000 1000<=this bit is F125.0
________ F124.7_F124.0______<=this bit is F125.3
_________________F125.7___F125.0
So F125.3=ON
Hope this helps you?
Kind regards
Henny
Hello
FW124 HEX = 0 0 0 8
So F125.3=ON
Kind regards
Henny
Thanks Henny ,
yes it was F125.3 and i follow it and at last was a lubrication level switch :cry:
the point i learned how you determined the problem
FW 124 = Flag Word 124 = Flag ( Word = two bytes ) 124 & 125 = Flag ( one byte = 8 bit ) = F124.7 < F124.0 & F125.7 < F125.0
Change 0 0 0 8 from HEX to Binary
0 = 0000
8/2 0
4/2 0
2/2 0
1 1
8 = 1000
this lead to
0000 0000 0000 1000
compare the signal 1 to F in same place = F125.3
Hello mitakka ,
Hope i could learn more in PLC all Ver. but the way is too long and am just started
Hello, I am trying to get a Yokogawa Hart pressure Transmitter and a Rosemount Temp Transmitter to read on a 1769-IF4 module on an L33ERM...
376
Please help me, I have solve many week but still not solve it. I found trouble of factory talk studio when I set tag by browse address of OPC...
117
Hello Everyone, i Have im my Industry a Endress & Hauser Promag400 this has a screen that constantly have that error, it says to wait, somebody...
476
After replacing the 70 with the 525, the PLC can read from the drive and recognizes it as online, but no commands are being listened to. PLC is...
551