Old January 9th, 2019, 04:45 PM   #1
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 104
monitor rslogix 5000 a tag

Hi,Guys:
we want to monitor a tag (PF525 drive output current) when drive output current is over the threat point at what exact time, we can use trend, the problem is we don't know when it happens, it could be once a week or twice a week, it very hard to trace it. we may use HMI to set up a alarm, but we didn't find a trigger point yet.
anybody has a idea?
thanks!
  Reply With Quote
Old January 9th, 2019, 05:06 PM   #2
scott.lawrence
Member
United States

scott.lawrence is offline
 
Join Date: Feb 2010
Location: Oklahoma
Posts: 170
you could write trap logic to let you know when & to what value the current exceeds the alarm/setpoint
  Reply With Quote
Old January 9th, 2019, 05:48 PM   #3
beethoven_ii
Lifetime Supporting Member
United Kingdom

beethoven_ii is offline
 
Join Date: Nov 2006
Location: England
Posts: 343
Assuming you're using Logix5000 you could set up a Message instruction to do a parameter read and read parameter 3 from the drive. Divide the value you get back from the drive by 100 and that will give the actual current of the drive in amps. Compare this to your limit and use the comparison to trigger an alarm if it ever goes above your limit then you'll have a log of when it happens. You could also compare the actual current value to another tag for the peak value so you'll know what the highest value the current has been.
  Reply With Quote
Old January 9th, 2019, 05:48 PM   #4
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 104
we want to know when the drive output current is over our set point.
for example: the drive output current is over 6A (set point) at 6:39 PM 1/9/2019, in fact we want to know another tag activity after this moment.If we don't use HMI.
Thanks!

Last edited by mike3475; January 9th, 2019 at 05:53 PM.
  Reply With Quote
Old January 9th, 2019, 06:17 PM   #5
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,160
You can use a GSV instruction to get the PLC's time, when you get your over current condition, save a copy of the current time.

http://www.plctalk.net/qanda/showthread.php?t=75629
  Reply With Quote
Old January 9th, 2019, 07:20 PM   #6
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 104
got you.
thanks everyone!
  Reply With Quote
Old January 9th, 2019, 09:06 PM   #7
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 104
http://bryceautomation.com/index.php...wallclocktime/
  Reply With Quote
Old January 10th, 2019, 07:59 PM   #8
ArtWalls
Member
United States

ArtWalls is offline
 
Join Date: Apr 2016
Location: Miami, Arizona
Posts: 53
We implemented a poor man’s version of value trapping using the built-in digital alarms logged to an SQL server. The almd instructions allow for extra tags, we point them to the relevant tags in the PLC. After the fact, we look at the alarms in SQL and can tell exactly what tripped them, and when.
  Reply With Quote
Old January 12th, 2019, 12:33 PM   #9
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 104
Thanks!
I never use ALMD instruction before, anybody has any example for ALMD instruction?

Thanks!
  Reply With Quote
Old January 12th, 2019, 04:48 PM   #10
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 739
Keep it simple .. When your current > Your set point, use the RE to write the date time to an alarm time.
  Reply With Quote
Old January 12th, 2019, 07:04 PM   #11
ArtWalls
Member
United States

ArtWalls is offline
 
Join Date: Apr 2016
Location: Miami, Arizona
Posts: 53
We put an almd instruction on a rung and set up the conditions ahead of it. Create the alarm tag, then use 0,0,0,1 as the parameters. Open the alarm definition, put in a descriptive message. Then, add any related tags. In your case I would put the drive current, the setpoint if it changes, and the other tag you were concerned with. When the rung goes true, the alarm will trigger. If you are going to an SQL server, a timestamp will automatically be captured.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Packing Data Into a Tag ndzied1 LIVE PLC Questions And Answers 8 January 12th, 2016 01:22 PM
RSLogix 5000 V16, 17, 18 Tag Database Print Out ebolbol LIVE PLC Questions And Answers 0 October 28th, 2015 04:33 PM
Logix 5000 install problem smiller LIVE PLC Questions And Answers 16 May 26th, 2015 09:47 PM
Clearing String Tag in Logix 5000 Structured Text pittpanther LIVE PLC Questions And Answers 2 August 27th, 2012 05:33 PM
Parsing out a tag name in RSLogix 5000 blueagate LIVE PLC Questions And Answers 6 March 26th, 2011 11:04 AM


All times are GMT -5. The time now is 07:23 PM.


.