Math status flag not assigned within the rung.
i tried to use S:V bit today but keep getting the error.
i am using studio5000
Old September 5th, 2018, 04:29 PM   #2
Dravik
United States
Dravik is offline
I haven't seen that error exactly but the newer processors only support the S:V bit being in the same rung as the instruction you are checking.
Old September 5th, 2018, 06:48 PM   #3
Geospark
Ireland
Geospark is online now
Geospark's Avatar
Quote:
Yes, at Studio 5000 v27 this little "enhancement" was added. But more specifically, you can only add math status flag instructions, such as XIC S:V, on a rung where the arithmetic instruction(s) you are checking precedes the math status flag instruction. Any rung arrangement where the math status flag is examined before the arithmetic instruction(s) is invalid and will not verify.
1023320 - Math status flag behavior change in Studio 5000 version 27
Access Level: TechConnect
Quote:
Originally Posted by carlostana8437@gmail
...i am using studio5000
Are you using Studio 5000 v27 or newer?
Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
Old September 10th, 2018, 11:40 AM   #4
Philippines
Regards,
George
V30+. i used to be able to use S:V without a math instruction before it but now it wont let me. is there a work around this.
Old September 14th, 2018, 12:24 PM   #5
Geospark
Ireland
Geospark's Avatar
No. There is no direct workaround. If using Studio 5000 Logix Designer v27 or newer you must place an arithmetic instruction, which will produce a math status flag, before any instruction instances which will consume a math status flag (S:V, S:C, S:N, or S:Z).
As an indirect workaround, you can use the S:V operand in an instruction after the intended arithmetic instruction, as they now expect you to do, and then at the end of the rung assign a user-defined overflow condition BOOL tag to an output instruction.
Example:
XIC Execute_ADD ADD myTagA myTagB myTagC XIC S:V OTE myADD_SV
If the ADD instruction were to overflow, then myADD_SV will be set to "1".
Then, where you would like to use the S:V operand for overflow status, for this particular arithmetic instruction, you can use myADD_SV instead and no arithmetic instruction needs to be present on the rung.
If you need to add a general S:V operand, where you need to evaluate if any overflow is active, to a rung where there are no arithmetic instructions, then you could create a DINT tag Prog_SV especially for user-defined overflow status for the particular program. The DINT will provide 32 x BOOL tags for use as individual user-defined overflow tags. These BOOL tags are then used throughout the program similar to the example above. You can then compare the entire DINT as an integer value (GRT>0) and if one or more of the overflow BOOLs within the DINT are set to "1" then the DINT value will be a non-zero value. This evaluation could set a BOOL tag, say Sys_SV. The status of Sys_SV should then tell you if there is currently any overflow conditions in the program, similar to how the S:V operand would tell you.
There may be other considerations if attempting to implement this or indeed other methods, but that is the bones of it.
Regards,
George
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
SLC 50/4 minor error bit Deer LIVE PLC Questions And Answers 19 November 21st, 2017 11:13 AM
PLC rung scan implications bernie_carlton LIVE PLC Questions And Answers 29 May 31st, 2015 01:57 PM
Start of Scan Beryl LIVE PLC Questions And Answers 31 September 25th, 2003 11:11 AM
rookie needs some help. system design timbo4255 LIVE PLC Questions And Answers 37 September 18th, 2003 07:20 AM