Rslogix 500

stu

Member
Join Date
Aug 2005
Location
England
Posts
772
Has anyone had an issue with rslogix 500 where if you do an online edit and then save after the change it fails and throws you offline and then you have to browse the file and upload again ?? Sooo annoying is there a cure
 
Stu
It sounds like you an uncommitted edit in the ladder someplace.
look for a rung that is under edit but not committed or saved
 
I have had this happen.
I had it happen when someone else made a copy of the program while I was online and made an edit - very messy.

I can't remember, but you can do a search for edits.
i'll try to find it if I have time.
duty calls and I goto go.
james
 
That sounds a lot like the well-known RSLinx CIP connection maximum issue in RSLinx Classic. The solution is a reconfiguration in RSLinx.

https://rockwellautomation.custhelp.com/app/answers/detail/a_id/32963

The basic problem, expressed as a parable:

"I need to a ladder to work on that fixture 12 feet up the wall"
"Sure, here's four 3-foot ladders."
"Shouldn't we secure them to one another instead of just stacking them on top?"
"Naw, you'll be fine"
*CRASH*
 

Similar Topics

Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
Replies
1
Views
113
I would like to copy register N61:131 thru N61:147 into ST252:0 I keep failing What happens is I copy into ST252:0,1, 2 etc. What am i missing...
Replies
18
Views
485
I'm trying to fix a mess of code on an older machine that's running a Micrologix 1400 and an RS232 ASCII barcode scanner. The previous guy had...
Replies
3
Views
306
I'm not super familiar with the Micrologix line of processors, but I am pretty familiar with RSLogix 500. I'm trying to simply copy a string to...
Replies
4
Views
260
I have been using RSLogix 500 version 9 for a long time now. I am about to need to move to something else Rockwell related to cover the...
Replies
8
Views
907
Back
Top Bottom