Nov 2003
Posts
100
Why are Safety Switches drawn in the literature showing and labeling NO contacts NC. In other words if you put a meter across the contacts marked NC in the un-actuated position it reads open. I assumed I had the wrong switch till I remembered seeing it on other safety switches and checked it. The way I read the mechanical drawing it looks like the contacts are open when actuated as well but apparently I am missing something. Maybe it's obvious but it seems confusing to me. Would someone be kind enough to explain this?

Thanks
Bill
 
No, I don't think you are missing anything. The way it was explained to me is that with safety gate switches where a tongue is inserted to actuate the switch, the "normal" condition is the "safe" condition. I agree this is opposite of the way we normally think.
 
Emergency Stop inputs are programmed as if they are normally open contacts, (held closed). This is so that they 'fail safe'. Any break in the circuit signals an emergency situation. 'Closed circuit = no problem'. If it were wired as closed circuit = problem, a broken wire would prevent detecting a fault = doesn't 'fail safe'. Limit switches for axes are also usually normally closed, so that loss of continuity indicates a problem vs. presence of a signal indicating a problem.
 
Why are Safety Switches drawn in the literature showing and labeling NO contacts NC. In other words if you put a meter across the contacts marked NC in the un-actuated position it reads open. I assumed I had the wrong switch till I remembered seeing it on other safety switches and checked it. The way I read the mechanical drawing it looks like the contacts are open when actuated as well but apparently I am missing something. Maybe it's obvious but it seems confusing to me. Would someone be kind enough to explain this?l
Yes, like Steve said, at first it does appear odd, but if you think of them like an E-stop, it makes sense. E-stops use normally-closed contacts, and are shown on diagrams in their 'un-actuated' state (released, with contacts closed). If you think about it, a guard switch's 'un-actuated' state would really be with the actuator inserted. When you open the door, the switch is actuated, just like an E-stop.

🍻

-Eric
 

Similar Topics

Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
Replies
5
Views
226
Hey guys, the scenario is: I have already completed the drawing package for my system utilizing an A-B 440R-N23126 (Minotaur) safety relay. SoS...
Replies
0
Views
128
I've ready through the the previous posts, and we've worked with safety design for a long time. In the past, we worked with Pilz directly, and...
Replies
9
Views
542
So first off I know everyone hates directly answering safety questions and I want to start by I will take no ones opinion as rule but looking for...
Replies
12
Views
1,359
Hi all, I'm working on a safety circuit and had some question about fusing. Incoming supply - 120V/15A Power supply - PSL-24-060...
Replies
5
Views
561
Back
Top Bottom