Symbol Descriptions RSLogix 500

ajb1131

Member
Join Date
Feb 2006
Location
Minnesota
Posts
3
I was wondering how to view the descriptions in rslogix 500.
When i go online i cant see them.

Thanks
 
Last edited:
Right click on any blank space in the ladder editor window.

Select "Properties"

Select "Comment Display" tab.

In the "Symbols" areas tick the "Show Symbols" box, then
you can choose either "Show Addresses and Symbols" or "Show Symbols Only"

(Personally I prefer to put Symbols on everything and select "Symbols Only" and that way I don't have to think too much about the Addresses.)
 

Similar Topics

I'm Loosing Descriptions of PLC5 Symbols when I go online with PLC. Ussually I can merge the files, except for this time it blows by the pop up...
Replies
4
Views
4,115
Hello everyone, Recently, my Archestra IDE shut down while I was editing. After restarting the IDE, I noticed warning symbols under my opened...
Replies
1
Views
96
I was looking for this function, so that i doesn´t need to do it in the PLC. If there are an alarm in the alarm list, i want to flash the...
Replies
2
Views
496
Hello, fairly new to plcs I’m tasked with installing a PE to a micrologix1200, in the attached picture I/14 is the PE I’m installing it’s going to...
Replies
6
Views
939
Hello Thank you all for your support. I am actually experience same issues with TIA portal V17 update5 as well as V18. The problem is with the...
Replies
0
Views
795
Back
Top Bottom