I did have the problem on test connection when I tried to load the FX2N program to the FX3U, same message, after I converted it I still had the message when I tried to download the program (well I think it was the same message but not sure), I selected both the PLC parameter & program then it allowed me to download. As I said I cannot try on an FX2N as I do not have one handy, the program without modification did download to the simulator though without errors, I don't quite know why. There does seem to be some bad programming practices within the program though, the transfer to/from the high speed counters to/from D memory is not quite correct, the counters C200 up are 32 bit counters so doing a 16 bit transfer is not quite right and on my FX3U it faulted. on one counter transfer they did a move from the counter to D700, however, D701 is not used elsewhere in the program so they could have done a 32 bit transfer using DMOV instead of MOV. The program I sent you has this mod on the two counters. there are two other errors (minor so do not stop the PLC) one is where they do a floating point math on some D registers in the D42> range I do not know why this shows a minor error "address out of range" or something like that. but it does not stop the program or affect the calculation.
I will look to see if I have a 2N processor in my junk cupboard that works.
EDIT: Not got an FX2N but to my surprise I have a new (well was when purchased) Micrologix 1500 2 port PLC still in it's anti static bag & a used ML1000