I have s7-400 plc with ET-200M station as a slave..
When the power for ET-200M is reset, then the plc goes to stop mode..
Which organization block (OB?) do i need to prevent it from stopping?
Please help!
Thanks! :)
Try OB86 "Rack error", OB87 "Comm error", or OB122 "IO error".
But to be absolutely sure, open up the CPU diagnostics while online and an active DP error (ET200M is shutdown). The diagnostic buffer will tell you exactly which OB you are missing.
Hi.
Adding an empty 0B86(loss of rack fault) will prevent your PLC going into stop mode when the power to the ET200 is cycled.
Hope this helps
Fiona.