Old October 16th, 2020, 11:14 AM   #1
unsaint33
Member
United States

unsaint33 is offline
 
Join Date: Sep 2019
Location: MInnesota
Posts: 43
SLC500 occasional CPU fault toggling

We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and verified every I/O terminal and comm with HMI. However, once in a while, its CPU fault LED comes on for a second. Then it goes away & PC RUN LED comes back on, and everything working again like nothing happened. I should return it, right?
  Reply With Quote
Old October 16th, 2020, 11:26 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,726
Quote:
Originally Posted by unsaint33 View Post
We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and verified every I/O terminal and comm with HMI. However, once in a while, its CPU fault LED comes on for a second. Then it goes away & PC RUN LED comes back on, and everything working again like nothing happened. I should return it, right?
Yes, I think so. I don't know of any way a CPU fault can be cleared and the unit return to run mode by itself without using programming software or cycling the keyswitch. I don't remember if the fixed SLCs even have a key switch.

Maybe the PLC power is intermittent internally and it is configured to go to run mode on power up...
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.
  Reply With Quote
Old October 16th, 2020, 11:27 AM   #3
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 2,367
I would, SLC's are renowned for faults after a number of years, generally rack or PSU faults, Rack is common for intermittent faults mainly because of either dry joints or bad connectors (I suspect heat over time or vibration on this one), aging components in the PSU are common.
One thing you can try is removing & replacing cards a few times to effectively "clean" the contacts, I have had success doing this & using contact cleaner, however, using cleaning solution would probably invalidate your warrantee.
  Reply With Quote
Old October 16th, 2020, 12:36 PM   #4
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 305
I definitely would try to replace that shoebox of a PLC.

Get either a 5/03 or 5/04 at least, or 5/05 if you want Ethernet.

Better, but they still have trouble with racks or analog cards taking down the power supply, shorting out the battery circuit when off and wiping the porgram, or just bein PITA's.
  Reply With Quote
Old October 16th, 2020, 12:43 PM   #5
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,914
That unit was a "brick" style so it usually didn't have I/O modules (although you could add on up to 2 with an expansion unit). There is no key on these. You must use the software to change the mode or clear a fault. I suspect that they did have a fault routine though which would allow the controller to reset a fault, but that should never allow the fault light to appear. Once that light comes on, the PLC shuts down and it cannot restart itself.

Either the fault light is just a glitch and the unit is never actually faulting, or you've got a bad controller. Either way, I would return/replace it.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old October 16th, 2020, 09:28 PM   #6
JaxGTO
Supporting Member
United States

JaxGTO is offline
 
Join Date: Apr 2009
Location: Kalieefornia
Posts: 820
I thought if you have a Fault routine that you can programmatically reset some faults and the program will continue to run. Faults like the overflow that most people have a hot branched OTU of.
__________________
I have to use Rockwell Software!
  Reply With Quote
Old October 17th, 2020, 08:11 AM   #7
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,914
Yes you can, but the red fault light will not turn on if the program clears the fault. The fault light only turns on when the controller has shut down.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old October 17th, 2020, 09:26 AM   #8
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,179
Quote:
Originally Posted by unsaint33
I downloaded a program to it and verified every I/O terminal and comm with HMI.

I am with everyone else and send it back but... just out of curiosity, remove everything and the program then does it still do it?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old October 17th, 2020, 12:32 PM   #9
lee1968nh
Member
United States

lee1968nh is offline
 
Join Date: Nov 2010
Location: NH
Posts: 69
The SLCs will fault after awhile if there is no fault...it is just their thing. So long w/o a fault, it must be a fault! J/k of course.
  Reply With Quote
Old October 22nd, 2020, 12:53 PM   #10
unsaint33
Member
United States

unsaint33 is offline
 
Join Date: Sep 2019
Location: MInnesota
Posts: 43
thank you for replies. I am going to send it back. But just out of curiosity, I want to count how many times it faults in a day or so. So, I wrote one rung program with S:1/15 first pass XIC and CTU OTE. I downloaded it to the PLC and power cycled few times. I figured that was simulating the CPU faulting since whenever I power up the CPU fault LED comes on first for a second for so before it goes off. I went on online and the counter acc was still 0. Can you tell me a program that can count the CPU faults? Thanks.
  Reply With Quote
Old October 22nd, 2020, 01:53 PM   #11
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 305
It might be that during the first scan counters and timers are automatically reset, so if you are using First Scan to count a counter it can't.

At the end of ladder 2 put XIC S:1/15 (FirstPass) OTE B3:0/15 (SecondPass) (or any not-used bit)

Then at the start of ladder 2 XIC SecondPass and CTU after the first scan is done.

EDIT: It might also be that the CPU is not actually faulting and stops scanning, so there won't be a FirstPass.
  Reply With Quote
Old October 22nd, 2020, 04:57 PM   #12
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,179
There is such a thing as a Fault Routine, the PLC will run the routine for one scan after the fault happens, I think you would need to use this and store it in a non volatile memory... I remember this from a long time ago but never researched how to program it

Quote:
When designating a subroutine file, the occurrence of recoverable or
non-recoverable user faults causes the designated subroutine to be executed
for one scan.
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old October 22nd, 2020, 08:34 PM   #13
lee1968nh
Member
United States

lee1968nh is offline
 
Join Date: Nov 2010
Location: NH
Posts: 69
Quote:
Originally Posted by geniusintraining View Post
There is such a thing as a Fault Routine, the PLC will run the routine for one scan after the fault happens, I think you would need to use this and store it in a non volatile memory... I remember this from a long time ago but never researched how to program it
Has anyone actually used the 'fault' routine? I admit I never have and am quite skeptical if it would even work.
  Reply With Quote
Old October 22nd, 2020, 08:41 PM   #14
lee1968nh
Member
United States

lee1968nh is offline
 
Join Date: Nov 2010
Location: NH
Posts: 69
One thing that cranked me about AB is CLX would and may still will fault if timer ACC is negative? Why oh why the hell why? All that means it the timer has expired...maybe even long ago. Always felt like a big-brother, we know better kind of thing. I disdain that feature. Dammit if the ACC is less than Present value, it is what I wanted it to be. Shutting down a process because of that(fault) is a software engineer's(AB) heavy-handed misconception. Yea, AB has bitten me in the but with "major faults" several times. I do not respect the "major fault" so-called feature. Really really don't.
  Reply With Quote
Old October 22nd, 2020, 08:49 PM   #15
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 305
Let me add a rant about the processor faulting if a pointer goes above an array dimension.



just flag a minor error that it can't do that and go on running the machine for the customer so they can make some money off their capital investment that could be more than their house or Lamborghini cost.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Is a major fault stored in the CPU after someone goes from RUN->PROG->RUN to reset jendrus LIVE PLC Questions And Answers 18 July 24th, 2012 10:38 AM
Blinking CPU Fault Light, SLC 500 EmpireBuilding LIVE PLC Questions And Answers 5 February 6th, 2011 11:54 PM
CPU 416-2DP fault indicator Eng.Abdo LIVE PLC Questions And Answers 16 July 24th, 2010 02:54 PM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 03:55 PM
Fanuc D3-330 CPU FAULT Martin IRL LIVE PLC Questions And Answers 8 April 22nd, 2003 04:59 AM


All times are GMT -4. The time now is 02:17 AM.


.