I have a PLC5 rack that had a power supply go out. Changed power supply and unable to communicate with processor with the exception of seeing it in RsLinx. No fault light on processor but when trying to go online with it it shows faulted and gives me the error in the attached image. I am connecting to it through a ControlLogix ENBT and DHRIO module. Keyswitch is in Run position. What am I missing?
Old October 17th, 2020, 09:20 PM   #2
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Going online with a faulted controller needs the same sort of resources as making an edit, so you can't do it with the keyswitch all the way in hard RUN mode.
The phrase "Check for keyswitch in RUN mode" means "it can't be in RUN mode" not "check to be sure it is in RUN mode".
Switch to PROG mode cycle power, and try again.
Old October 18th, 2020, 09:18 AM   #3
Ron Beaufort
United States
Ron Beaufort is offline
Ron Beaufort's Avatar
another point ...
since the RSLinx doesn't appear to be showing a NAME for the processor, then the processor MIGHT have completely lost its program ... "dead in the water" ... this usually occurs when the battery is dead - and the power is turned off ...
if that's the case, you'll need to download the program ...
after you cycle the keyswitch, recheck the PROC light (LED) on the front of the processor ... is it SOLID red - or FLASHING red? ...
__________________
2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp - Retired | 2-B |
I once was lost, but now am found, was blind, but now I see.
Old October 18th, 2020, 11:04 AM   #4
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
You didn't specify in your post whether the PLC was the 5/30 or the 5/80. I think we are assuming it is the 5/80 since you said you can see it in RSLinx. If it is instead the PLC-5/30 you are trying to talk to, please let us know.
You mentioned there is no fault light on the CPU. I assume you are saying there are no red lights on the CPU. If the keyswitch is in Run, you should see a solid green PROC light. If it were faulted, it would be flashing or solid red. RSLinx seems to think it is faulted.
But as Ron pointed out, not seeing a name for that CPU would usually indicate a fault where the controller has dumped the program. That would show a solid red PROC light (non-recoverable fault) on the CPU. If that is the case then you cannot go online with the controller since there is no program loaded. It cannot recover from this, The program must be reloaded.
If the key is in the hard run position, the fault cannot be cleared and you can't reload the program. Move it to the REM position and the software will be allowed to clear the fault.
If the light is flashing red, then the program is still there but there is a recoverable fault. With those, the existing program is intact so you can recover from this. But, by all indications, this is not the case.
OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
Old October 18th, 2020, 11:36 AM   #5
I_Automation
United States
I_Automation is offline
I_Automation's Avatar
I had something similar on a SLC that was running with RSLinx.
Had to close RSLinx, delete the harmony files, then reopen it. Somehow the fault locked the reading in RSLinx.
Here's how to do that - it does NOT delete your drivers or settings, only the WhoIs display information that is recreated when opened.
EDIT - I just use the manual method, delete 2 files in the Rockwell Software folder.
Old October 18th, 2020, 10:33 PM   #6
micky
United States
micky is offline
micky's Avatar
The PLC had lost it's program. Whenever Ron mentioned the name of the PLC missing I went back to RsLinx and noticed that only the default configured channel was communicating on the DH network and not the other which was also configured to communicate on the DH network. Went today switched it to REM and was able to download backup copy of program. All is good.
Thanks guys for the extra set of eyes and bits of troubleshooting hints.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
What can i do to get better at coding controls logics? Jrivers010 LIVE PLC Questions And Answers 54 August 23rd, 2017 06:08 PM
ENET Scanner is faulted and cannot see PLC through Ethernet aru.atsrobotics LIVE PLC Questions And Answers 3 July 19th, 2017 04:26 PM
PLC Update - Back Issues Collection Now Available! Phil Melore LIVE PLC Questions And Answers 11 October 22nd, 2015 03:17 AM
Siemens PLC won't auto-run after power-up Lamboom LIVE PLC Questions And Answers 5 August 19th, 2014 05:32 PM
PLC 5 Processor Faulted when PID enabled. Need Help sparkytex LIVE PLC Questions And Answers 4 April 16th, 2014 08:52 PM