Old October 16th, 2020, 11:14 AM   #1
unsaint33
Member
United States

unsaint33 is offline
 
Join Date: Sep 2019
Location: MInnesota
Posts: 42
SLC500 occasional CPU fault toggling

We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and verified every I/O terminal and comm with HMI. However, once in a while, its CPU fault LED comes on for a second. Then it goes away & PC RUN LED comes back on, and everything working again like nothing happened. I should return it, right?
  Reply With Quote
Old October 16th, 2020, 11:26 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,725
Quote:
Originally Posted by unsaint33 View Post
We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and verified every I/O terminal and comm with HMI. However, once in a while, its CPU fault LED comes on for a second. Then it goes away & PC RUN LED comes back on, and everything working again like nothing happened. I should return it, right?
Yes, I think so. I don't know of any way a CPU fault can be cleared and the unit return to run mode by itself without using programming software or cycling the keyswitch. I don't remember if the fixed SLCs even have a key switch.

Maybe the PLC power is intermittent internally and it is configured to go to run mode on power up...
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.
  Reply With Quote
Old October 16th, 2020, 11:27 AM   #3
parky
Member
United Kingdom

parky is online now
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 2,342
I would, SLC's are renowned for faults after a number of years, generally rack or PSU faults, Rack is common for intermittent faults mainly because of either dry joints or bad connectors (I suspect heat over time or vibration on this one), aging components in the PSU are common.
One thing you can try is removing & replacing cards a few times to effectively "clean" the contacts, I have had success doing this & using contact cleaner, however, using cleaning solution would probably invalidate your warrantee.
  Reply With Quote
Old October 16th, 2020, 12:36 PM   #4
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 286
I definitely would try to replace that shoebox of a PLC.

Get either a 5/03 or 5/04 at least, or 5/05 if you want Ethernet.

Better, but they still have trouble with racks or analog cards taking down the power supply, shorting out the battery circuit when off and wiping the porgram, or just bein PITA's.
  Reply With Quote
Old October 16th, 2020, 12:43 PM   #5
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,911
That unit was a "brick" style so it usually didn't have I/O modules (although you could add on up to 2 with an expansion unit). There is no key on these. You must use the software to change the mode or clear a fault. I suspect that they did have a fault routine though which would allow the controller to reset a fault, but that should never allow the fault light to appear. Once that light comes on, the PLC shuts down and it cannot restart itself.

Either the fault light is just a glitch and the unit is never actually faulting, or you've got a bad controller. Either way, I would return/replace it.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old October 16th, 2020, 09:28 PM   #6
JaxGTO
Supporting Member
United States

JaxGTO is offline
 
Join Date: Apr 2009
Location: Kalieefornia
Posts: 820
I thought if you have a Fault routine that you can programmatically reset some faults and the program will continue to run. Faults like the overflow that most people have a hot branched OTU of.
__________________
I have to use Rockwell Software!
  Reply With Quote
Old October 17th, 2020, 08:11 AM   #7
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,911
Yes you can, but the red fault light will not turn on if the program clears the fault. The fault light only turns on when the controller has shut down.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old October 17th, 2020, 09:26 AM   #8
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 7,169
Quote:
Originally Posted by unsaint33
I downloaded a program to it and verified every I/O terminal and comm with HMI.

I am with everyone else and send it back but... just out of curiosity, remove everything and the program then does it still do it?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old October 17th, 2020, 12:32 PM   #9
lee1968nh
Member
United States

lee1968nh is offline
 
Join Date: Nov 2010
Location: NH
Posts: 64
The SLCs will fault after awhile if there is no fault...it is just their thing. So long w/o a fault, it must be a fault! J/k of course.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Is a major fault stored in the CPU after someone goes from RUN->PROG->RUN to reset jendrus LIVE PLC Questions And Answers 18 July 24th, 2012 10:38 AM
Blinking CPU Fault Light, SLC 500 EmpireBuilding LIVE PLC Questions And Answers 5 February 6th, 2011 11:54 PM
CPU 416-2DP fault indicator Eng.Abdo LIVE PLC Questions And Answers 16 July 24th, 2010 02:54 PM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 03:55 PM
Fanuc D3-330 CPU FAULT Martin IRL LIVE PLC Questions And Answers 8 April 22nd, 2003 04:59 AM


All times are GMT -4. The time now is 06:39 AM.


.