K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
 
K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
welcome to the site
Can you please check the date of the last post

2009 is very old
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/

welcome to the site
It is great to see new input from new members.
but
please check the original post date
this is from 2007 (5 years old);)
 

Similar Topics

Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,658
I recently uploaded an aplication from a Panel View, created a new screen and now that I've downloaded it to the Panel View, all the texts have...
Replies
9
Views
155
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
4
Views
137
Hi All, So I have a main routine with an instruction that's executed by XIC "Run" I have a JSR located on a rung below it. In the logic for that...
Replies
6
Views
244
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
104
Back
Top Bottom