When the PID block is used in S7 1200 software, does it need to be called from anywhere or just inserted into a network. The help is a bit vague about this.
The screenshot how it looks online, but the PID does not seems to be active.
pid1200.jpg
 
Last edited:
The old manual just pointed you to the online help and the online help was as much use as a chocolate teapot. The new manual for Step 11 has a lot more information about the PID loop.

Excerpt:

Note
Execute the PID instruction at constant intervals of the sampling time (preferably in a cyclic OB).
Because the PID loop needs a certain time to respond to changes of the control value, do not calculate the output value in every cycle. Do not execute the PID instruction in the main program cycle OB (such as OB 1).
 
Call it out of ob35. Also in your instance db, check the mode and make sure the pid is set for auto. It is a mode number.
 
Thanks to all

Thanks to all who helped me, I was getting somewhere near, but not close enough,
Wolverine that link you sent me fills all the gaps, I can go on now to do some serious stuff.
I am puzzled why the stuff was not included in the kit I bought from Siemens.

Thanks a million.
I can sleep tonight now.(y)🍺
 
I felt the same way when I purchased mine, and when you check their web site there is several different forums that you need to find. And then there is also the Pod Casts, example programs when you can find them and what you can also find on utube.

Tom
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
53
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
114
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
84
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
Replies
1
Views
140
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but...
Replies
5
Views
205
Back
Top Bottom