How to change Firmware on a 16 Axis Serco's Servo Module 1756-M16SE

Good Evening ,

We have a number of Kinetix 6000 Servo drives ( fiber ) that fault out from time to time . I would like to change out the ControlLogix 16 Axis Serco's Module . The one that is in there is firmware 15.32 , but the replacement is firmware 15.37 , and it does not want to talk with ether the drives or the processor. How would I change the firmware on that card ? Also , the processor is ver. 16 . Would I change the firmware on the Serco's module to 16.0 ? With the new Serco's module , According to the plant electrician , the CP indicator is Flashing Red ( Looking for active nodes ) , Ring Status ( O ) Flashing Green ( The Ring , Drive , or Axis are not configured , but at least one has been identified ). The OK indicator is Flashing Green ( The module has passed internal diagnostics , but has not established communication)

Is this something you would ControlFlash for ? If so how would it be done ?

Thanks so much for your help.
  Reply With Quote
Old February 16th, 2017, 05:15 PM   #2
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,165
I've not used a sercos module on a Control Logix system before, but I do know that on a 1768 Compact Logix system, when updating the CPU firmware I also had to update the SERCOS module firmware to the same major revision before communications would resume. And since the SERCOS module gets it's configuration from the CPU, if it couldn't talk to the CPU to get it's configuration, it couldn't talk to any of the drives.

This is not quite the same as your problem, obviously, because the old SERCOS card had a different major revision to the PLC as well, and still worked. But I'd definitely be squinting suspiciously at firmware incompatibilities. My first move would be to take backups of everything and flash both PLC and SERCOS up to the highest possible revision. They both use ControlFlash for firmware upgrades.
  Reply With Quote
Old February 16th, 2017, 05:46 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,264
In general, you will want to run compatible versions of 1756-L55 or -L6x controller firmware and 1756-M16SE SERCOS motion module firmware, though it's not a "lock step" equivalency requirement or a narrow specific tested set like the Redundancy system.

I would use ControlFlash to put v16.023 firmware on the CPU and v16.002 firmware on the SERCOS module.

Both the 1756-L55 and 1756-L6x controllers had a stable firmware release at version 16.023. That's the one you want.
  Reply With Quote
Old February 16th, 2017, 08:15 PM   #4
Rob S.
Member
United States

Rob S. is offline
 
Join Date: Sep 2008
Location: Maryland
Posts: 585
Thanks for the information. I just received this email from the plant concerning
the issue we are having

" Josette checked the alarm history and it shows all the servo motors faulted out individually at the exact same time. Josette was able to see that the drives were showing a E-38 fault. On both incidents it required the power to killed and brought back up to get the wrapper to reset and run. "

This is the random E38 Ring we have been getting . I was going to replace the fiber optic cables , but seems to be a deeper problem to fault all the drives out.

Thanks,
  Reply With Quote
Old February 16th, 2017, 09:37 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,264
E38 faults on all the servos at the same time ? Almost definitely a damaged fiber-optic cable.

It can't hurt to upgrade your firmware to a nice stable release, but you're going to need to go after the fiber cables if you want a reliable system.

Note that you might not see in other places; when you upgrade motion modules, remove the CPU from the chassis. That keeps the CPU from interfering with the upgrade process by attempting to connect to the motion modules while they're rebooting between firmware chunks.
  Reply With Quote
Old February 16th, 2017, 09:44 PM   #6
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,165
Quote:
Originally Posted by Ken Roach View Post
Note that you might not see in other places; when you upgrade motion modules, remove the CPU from the chassis. That keeps the CPU from interfering with the upgrade process by attempting to connect to the motion modules while they're rebooting between firmware chunks.
That's an interesting point. Would putting the processor in Program mode achieve the same end, or does it still try to connect in Program mode?

I only ask because while it's easy to do this with a Control Logix chassis, it's a bit tricker with a Compact Logix chassis like the one I mentioned before. Still doable, of course, but not just as easy as unplugging it from the chassis!
  Reply With Quote
Old February 17th, 2017, 04:05 AM   #7
Rob S.
Member
United States

Rob S. is offline
 
Join Date: Sep 2008
Location: Maryland
Posts: 585
I'm sorry Ken and ASF. Can you rephrase this. I don't understand what you mean .

"Note that you might not see in other places; when you upgrade motion modules, remove the CPU from the chassis. That keeps the CPU from interfering with the upgrade process by attempting to connect to the motion modules while they're rebooting between firmware chunks."

Thanks again for your help ,
  Reply With Quote
Old February 19th, 2017, 05:49 PM   #8
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,165
What Ken means (if I may take the liberty of assuming for a moment) is that your CPU is configured to look for, connect to and configure a SERCOS module. If you CPU is in the chassis and powered up, it'll do that continuously.

When you begin to flash the firmware to the SERCOS module, it will break the connection to the CPU. I'm not sure exactly how the CPU handles this, I should hope that the CPU gets some sort of message to say "I'm doing firmware now, stop trying to talk to me", and that it would do just that. But whether or not that happens, as part of the firmware upgrade, the SERCOS module will reboot at least once. When it reboots, the CPU will see it come back up and try to re-establish a connection to it. This could potentially interfere with the firmware upgrade process, as the module may need to re-boot several times during the procedure, and may not be finished updating when the CPU tries to connect to it and send over new configuration data.

As evidenced by the fact that I just recently performed a SERCOS module upgrade without removing the CPU, and it worked just fine, it's not a do-or-die requirement, but I can definitely see that it's a good idea to do it. Just like the way that when I'm flashing firmware on a CPU, I always remove it completely from the network so that no other PLC's, HMI's, drives, or anything else out there tries to butt in while I'm doing the upgrade and causes issues.
  Reply With Quote
Old February 19th, 2017, 07:41 PM   #9
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,264
That's an excellent explanation.

"Modern" ControlLogix and motion modules probably don't have this problem, but I encountered it enough in the L1 and M02AE days that disabling the CPU's ability to connect with the motion modules (by removing it or by flashing it first and not reloading the user program) is my standard operating procedure.

A couple of years ago I had to replace all the fiber optic cables on a SERCOS based v16 system because somebody had ordered ones that were too long, so they coiled them up and mashed down the cabinet door until it latched. All the cables easily passed optical attenuation tests, but there must have been one or two of them that attenuated too much when they were bent.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1756-M02AE 2 axis module replaceing problem Robotroc LIVE PLC Questions And Answers 3 July 24th, 2013 04:22 PM
1756 ENBT Module - Firmware detail jm.shafi LIVE PLC Questions And Answers 5 September 23rd, 2009 01:58 AM
FC AG_SEND and AG_RECEIVE cfbosch LIVE PLC Questions And Answers 10 December 3rd, 2008 03:00 AM
Analog Input underscale brucechase LIVE PLC Questions And Answers 11 January 3rd, 2007 11:13 AM
CL V15 - Sercos Module Issue curlyandshemp LIVE PLC Questions And Answers 2 September 15th, 2005 11:29 PM


All times are GMT -5. The time now is 12:02 AM.


.