Ethernet card not working in 1756 series.

So I have a Rockwell setup here with a (Control Logix) L62 and an EN2T card.

I can ping the card from the command line but RSLogix can't talk to it over Ethernet - only with USB. Also, the controller doesn't see anything else on the network.

I check the that the revision matches in both the General and Module Info tabs.

HELP!
  Reply With Quote
Old February 17th, 2017, 01:24 PM   #2
Mispeld
Member
United States

Mispeld is offline
 
Join Date: Feb 2017
Location: VA
Posts: 100
Does the EN2T's IP address appear in the RS-Linx "RSWho" browser window? Getting it appear there is your first step.
  Reply With Quote
Old February 17th, 2017, 01:31 PM   #3
RetiQlum
Member
United States

RetiQlum is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 23
Not when I don't have the USB connected. I can still ping it though.

The I have the local wired connection set to "Work" and the firewall configured to allow RSLinx, RSLinxNG, RSLinxShortcutAOA, RSLogix 5000 and Studio 5000 connections.
  Reply With Quote
Old February 17th, 2017, 01:51 PM   #4
Mispeld
Member
United States

Mispeld is offline
 
Join Date: Feb 2017
Location: VA
Posts: 100
I would make sure the ping response is really from the EN2T by disconnecting the network cable from that module and re-pinging the address. Assuming no response, reconnect and re-ping to get confidence the response is coming from that device. Then double-check the Ethernet driver configuration in RS-Linx for the correct IP of that module.
One thing that frustrates me with RS-Linx is having to wait for it to "see" a device manually added to the driver configuration. I have not found a way to force it to connect to a specific IP address, and would be interested if there is a trick to poke RS-Linx this way.
  Reply With Quote
Old February 17th, 2017, 01:55 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,163
A very common problem with browsing automation networks is if your PC is "dual homed", with both wireless and wired networks connected.

If you're using the EtherNet/IP driver, make sure it's configured to use your hardwired network connection.

A good troubleshooting step is to simply disable your WiFi connection, if you're using one.

VPN software also frequently interferes with the broadcast packets used by the EtherNet/IP driver; try the Ethernet Devices driver, which uses individual TCP connections to specified IP addresses, instead of browsing with a broadcast packet.
  Reply With Quote
Old February 17th, 2017, 02:09 PM   #6
RetiQlum
Member
United States

RetiQlum is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 23
Turns out to be something really simple.

RSLinx wasn't installed with Ethernet-IP drivers.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Ethernet card bb1fit LIVE PLC Questions And Answers 7 March 7th, 2014 09:44 AM
Ethernet Card Fault Control logix Densam LIVE PLC Questions And Answers 0 March 19th, 2013 05:17 PM
Maple Systems HMI5104TH copy files from SD card via ethernet Epy LIVE PLC Questions And Answers 3 November 17th, 2012 01:09 AM
Problem Ethernet Card with Siemens enault LIVE PLC Questions And Answers 6 June 18th, 2010 01:05 PM
1784-PCMK/B Card Health msinclair LIVE PLC Questions And Answers 6 August 13th, 2004 09:19 AM


All times are GMT -5. The time now is 07:10 PM.


.