need to set up to load applications to the PV1000 RS232/DH485 thru a SLC 5/04. Laptop is usin a PCMK to the DH+ on the SLC and the SLC is connected to the PV via a 2711-NC13. How do I setup for pass-thru?
Thankx,
glenn
 
Hi Glenn,

Firstly, it is possible.

If you can access this technote it may help to get you started...

17879 - Data Highway Plus to DH-485 pass-thru from SLC504 to Standard PanelView
Access Level: TechConnect

If not then do let us know and we can try to assist you directly.

It is a standard PanelView 1000 and not a PanelView Plus 1000, or other? What is the full catalog number for the PanelView terminal?

Note: The technote is using a 1784-KTX from the computer, whereas you are using a 1784-PCMK. However, it should be the same driver you select in RSLinx Classic for either interface device: 1784-PKTX(D)/PCMK for DH+/DH-485 devices.

Regards,
George
 
Last edited:
Geospark,
Don't have a Techconnect account...
I remember doing this several years ago, Have to set the "workstation" to pass-thru if i remember correctly
 
OK, the terminal is a PanelView Standard 1000.

The "workstation" would normally refer to your computer and this is not the node on the network that will perform the actual pass-thru, that will be the SLC 5/04.

DH+:

The PCMK will usually be node 0 on the DH+ network. The SLC 5/04 channel 1 DH+ port will typically be node 1 (default) but yours could be different.

The DH+ baud rate is typically set to 57,600 baud - make sure the PCMK and the SLC 5/04 are set the same.

DH-485:

The SLC 5/04 channel 0 configured to DH-485 is typically node 1 (default) on the DH-485 network but yours could be different. The PanelView terminal is typically node 2 on the DH-485 network, but again, yours could be different.

The DH-485 baud rate is typically set to 19,200 baud - make sure the SLC 5/04 and the PanelView are set the same.

In RSLogix 500 under "Processor Status" / "Chan 0" tab - make sure that both DH-485 pass-thru disable (S:34/0) & DF1 pass-thru enable (S:34/5) are set [0].

This means DF1 pass-thru is not enabled and DH-485 pass-thru is enabled.


Check the "Passthru Link ID" for both channel 0 and 1 in the SLC 5/04 - these should be set different to each other (default CH0=1; CH1=2)

Can you at least browse to the SLC 5/04 on the DH+ network in RSLinx Classic from the PCMK? Is this an existing setup or are you starting from scratch?

When it's working you should see both the SLC 5/04 and the PanelView terminal in RSLinx Classic.

Regards,
George
 
Last edited:
If you can get a PCMCIA memory card, or adapter and CF card, that is the fastest and most sure fire way to transfer programs to and from any Panelview Standard with a PCMCIA card slot (iirc, they all have one except the PV300 Micro).
 

Similar Topics

I have a mer or apa file for Pv1000 (2711p-rdt10c) and i need convert this files for Pv5000 (2715P-T15CD-K). Are exist a conversion tool for this...
Replies
1
Views
856
Hi, im looking to migrate a 2711-K10C10 to a 2711P-T12W21 Panelview Plus 7 Standard. I migrate the PV1000 application .pba file in FactoryTalk...
Replies
13
Views
1,932
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
Replies
1
Views
1,037
Hi, I'm investigating the feasibility of communication between a old PV standard display and a logix L5X controller via the controller serial...
Replies
3
Views
1,435
Hi all, Anyone manage to get this smorgasbord of hardware to cooperate with each other? PLC - Micrologix 1500 1764-28BXBAA CH1 config - DF1 Full...
Replies
2
Views
1,469
Back
Top Bottom