Old September 23rd, 2018, 10:10 AM   #1
PL_c
Member
Lithuania

PL_c is offline
 
Join Date: Apr 2018
Location: LT
Posts: 5
Common ground or 0V

Hi, I have two different power supplies.
First 5A DC, second 20A DC

I will use them for PLC's.

How i should connect them together.

Please look at pictures.

Thank you.
Attached Images
File Type: png Untitled.png (28.9 KB, 105 views)
  Reply With Quote
Old September 23rd, 2018, 10:31 AM   #2
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 565
You don't have to connect together, however, if you need the same "Reference Point" for both then you should connect as shown in figure 2.
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Old September 23rd, 2018, 10:59 AM   #3
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 86
you never need figure 1 ,since the 24V power suply primary side always isolated with secondary side +24V.

Last edited by mike3475; September 23rd, 2018 at 11:01 AM.
  Reply With Quote
Old September 23rd, 2018, 11:03 AM   #4
PL_c
Member
Lithuania

PL_c is offline
 
Join Date: Apr 2018
Location: LT
Posts: 5
I use seperate plc’s who are power supplied from different power supplies and these plc’s share with each other inputs/outputs.
  Reply With Quote
Old September 23rd, 2018, 11:34 AM   #5
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 277
Any power supply output needs a reference to ground. It can not be floating.
If it were floating and its cables pass next to other cables with strong dv/dt like those that use PWM, voltages in the range of thousands volts can be induced respect to earth in the floating side.

For avoid this the usually way is to connect the 0V output to ground but only at one point, usually at power supply output terminal, but never use the ground circuit as power supply common. The common must be a separate wire.

Of course to achieve this the power supply must have the output isolated from input. The same applies for transformers.
__________________
Suppanel HMI
  Reply With Quote
Old September 23rd, 2018, 08:21 PM   #6
kalabdel
Member
Canada

kalabdel is offline
 
Join Date: Feb 2015
Location: Ontario
Posts: 351
I don't get the purpose of #1 as both supplies are wired to the same neutral anyway, according to the schematic.

As for connecting both output commons together, yes if they share devices. An example is analog sensors powered by G1 and their output is connected to PLC inputs that is powered by G2. In that case both PLC Analog sensors need to share the same reference point/common.
And as Ife stated grounding has to also be considered.
  Reply With Quote
Old September 23rd, 2018, 10:00 PM   #7
kalabdel
Member
Canada

kalabdel is offline
 
Join Date: Feb 2015
Location: Ontario
Posts: 351
Quote:
Originally Posted by kalabdel View Post
both PLC Analog sensors need to share the same reference point/common.
correction:

both PLC and Analog sensors need to share the same reference point/common.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OK to Tie Powersupply Common to Chasis Ground? skyfox LIVE PLC Questions And Answers 53 September 6th, 2017 11:55 AM
Advice for connecting ground of RS 485 in PLC arbj LIVE PLC Questions And Answers 6 October 10th, 2015 02:30 PM
Grounding 0V of 24VDC System. Micrologix 1100 69FIREBIRD LIVE PLC Questions And Answers 2 November 28th, 2013 07:16 AM
Common 0V only on 2 x 24VDC power supplies qwsoftware LIVE PLC Questions And Answers 7 December 14th, 2009 08:45 PM
" do not care for AC connection " is this statement correct ?? magdyfayad LIVE PLC Questions And Answers 26 October 3rd, 2008 10:52 AM


All times are GMT -5. The time now is 03:46 PM.


.