We have a S5-PLC CPU 115U, and its running.
But, when I set the selector in Stop and then back again in RUN: CPU doesn't restart.

When I do an overall reset and then selector to run, plc is in run.
If I then download first the DB's and then the PB, OB and FB: PLC stays in run, and we can work.
But I want to know why I cannot make a cold/warm restart...

We work with the IBH-softec S5-S7 for Windows:
ISTACK-error: "coupling flag transfer list corrupted"
Does anyone knows this error?

I'v tried (after an overall reset-with selector in STOP) to download only the DB. Even then PLC stays in STOP when I set the selector in RUN.

See in attachment a picture of the ISTACK

IStack.jpg
 
Do you have a picture of the 1st ISTACK window? (not extended) It's also good to click the drop-down list where it says "coupling flag transfer list corrupted"

The closest description I find from the S5-115U manual is: "KOLIF - Interprocessor communication flag transfer list is incorrect." I don't know why IBH (S5 for Windows) decided to change the ISTACK descriptions.
 
Modules in the rack after CPU:
- 32 inputs
- 32 inputs
- 32 outputs
- 32 outputs
- 32 inputs

No IM360

See in attachment the first screen of the ISTACK.
Perhaps I have to try to see the IStack with the Siemens S5-soft?

ISTACK_1.jpg
 
See in attachment the Istack.
In the Istack, I dont see any error.
But the B-stck means a program error... where can I find the explanation of the HEX-codes??

Istack_1.jpg Istack_2.jpg BStack.jpg
 
This is the information about the BSTACK:

During program scanning, jump operations enter the following information in the block stack:
• the data block that was valid before program scanning exited a block;
• the relative return address. This address indicates the location at which program scanning continues after it returns from the block that was called.
• the absolute return address. This address indicates the location in the program memory at which program scanning continues after it returns from the block that was called.

Look at OB1 online (in STL), and I think it will show you the PLC memory addresses of the instructions in the left-hand column, and look for 9176. I think the PLC stopped at absolute address 9176, and the next expected instruction is at 9180. And the relative address is 000A (9180 - 9176 = 000A).

I thought the BSTACK function let you open to that spot in the program, but I could be wrong.
 

Similar Topics

i have a siemens 135u plc cpu which is in stop mode. the number of the processor is 6es59223ua11. i dont have a programmer so i need help on how...
Replies
8
Views
6,195
Hi everyone, I want to upload the program from my CPU317TF-2 DP to my PC via connecting to CP 343-1 Advanced since it has LAN ports and the CPU...
Replies
1
Views
123
Buona sera, Ho dei problemi nell' interfacciare PLC S5 con HMI 2a Gen. Siemens (ad esempio KTP400) tramite IBH Link S5++. il mio obbiettivo è solo...
Replies
0
Views
62
Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
Replies
0
Views
96
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
39
Views
2,065
Back
Top Bottom