Is it possible? communication between CP942H Siemens S5 PLC with ACS 800 ABB Drive??

drspanda

Member
Join Date
Oct 2005
Location
Damanjodi
Posts
155
Dear Drive Experts,

In our Mines division we are using S5 Siemens PLC with CPU:CP942H and we are now getting ACS800 ABB Drive, which supports Modbus communication.

I want to know is it possible to communicate with that drive by adding any additional hardware? if Yes where can I get that? I am from India.

As from local siemens representatives, they are asking for the upgradation to S7 PLC..
 
Siemens S5 and ACS800

In the Siemens S5 PLC you can use a 6ES5 308-3UC11 Profibus card and in the ACS800 use a RPBA Profibus card.
Then make the communication on Profibus.

The problem is to find a 6ES5 308-3UC11 card, but it is possible.
 

Similar Topics

I need to use serial to Ethernet converter to communicate serial (RS-232) device (LMS-200 SICK sensor) over ethernet. I am having IC695ETM001...
Replies
1
Views
3,087
We have Panelview 600 "Standard" on one of our machines which we got from supplier. We don't have documentation or software to upload/edit file...
Replies
5
Views
3,688
We planned on our network using an EN2T in our controllogix rack to talk to all the Point I/O, but I get the dreaded yellow triangle on all the...
Replies
3
Views
2,076
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
1
Views
111
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
0
Views
65
Back
Top Bottom