Not quite Plastic,
I'll wager our friend is using the Embedded Ethernet/IP adapter module but even if they were using the add-on dual port 25-COMM-E2P adapter module...
Out-of-the-box the PowerFlex 525 has the following default parameters for control and reference of the drive -
P046 [Start Source 1] - 1 "Keypad"
P047 [Speed Reference 1] - 1 "Drive Pot"
So whether using the Embedded EtherNet/IP module or the add-on dual port 25-COMM-E2P adapter module, a user must set those parameters away from the defaults to the correct option for the chosen Ethernet adapter...
Embedded EtherNet/IP -
P046 [Start Source 1] - 5 "EtherNet/IP"
P047 [Speed Reference 1] - 15 "EtherNet/IP"
25-COMM-E2P -
P046 [Start Source 1] - 4 "Network Opt"
P047 [Speed Reference 1] - 4 "Network Opt"
Long story short, the Embedded Ethernet/IP port is not the default for those parameters.
Regards,
George
I'll wager our friend is using the Embedded Ethernet/IP adapter module but even if they were using the add-on dual port 25-COMM-E2P adapter module...
Out-of-the-box the PowerFlex 525 has the following default parameters for control and reference of the drive -
P046 [Start Source 1] - 1 "Keypad"
P047 [Speed Reference 1] - 1 "Drive Pot"
So whether using the Embedded EtherNet/IP module or the add-on dual port 25-COMM-E2P adapter module, a user must set those parameters away from the defaults to the correct option for the chosen Ethernet adapter...
Embedded EtherNet/IP -
P046 [Start Source 1] - 5 "EtherNet/IP"
P047 [Speed Reference 1] - 15 "EtherNet/IP"
25-COMM-E2P -
P046 [Start Source 1] - 4 "Network Opt"
P047 [Speed Reference 1] - 4 "Network Opt"
Long story short, the Embedded Ethernet/IP port is not the default for those parameters.
Regards,
George