Old February 22nd, 2021, 06:38 PM   #121
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,356
Dead time is measured from the time the control output changes, the orange line, to the time the system responds.
You have the wrong definition of dead time.
There may be multiple dead times in a system but they can be combined into one.



I don't agree with quantizing the control output into such coarse steps.
Quantizing to steps may work if the update rate was faster. Then this would be like a multi step PWM.


A thousand curses on the person that designed this mess.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 22nd, 2021, 07:02 PM   #122
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317
@PeterN I understand what you are saying, and agree that, at a minimum, there may be better alternatives to stiction and other backlash and/or hysteresis issues.


But in the actual case the control valve will be initially behind the CV (deadtime), then ahead of the CV ("aheadtime" if you will), then behind, then ahead, etc. So from a practical standpoint, with the obviously much longer time constants in play, that will average out and behave as if deadtime is much smaller than system time constants, and so can be ignored with Td set to zero.
  Reply With Quote
Old February 22nd, 2021, 07:15 PM   #123
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,356
Quote:
Originally Posted by drbitboy View Post
But in the actual case the control valve will be initially behind the CV (deadtime), then ahead of the CV ("aheadtime" if you will), then behind, then ahead, etc. So from a practical standpoint, with the obviously much longer time constants in play, that will average out and behave as if deadtime is much smaller than system time constants, and so can be ignored with Td set to zero.
I shake my head. The PV can never respond to a change in the CV that hasn't happened yet.
This is the problem. Until you understand what you are controlling you will need to be lucky to get it to work and at least waste a lot of time like on this project.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 24th, 2021, 07:00 AM   #124
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,356
Did you give up?
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 24th, 2021, 07:47 AM   #125
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317
no, I thought I posted a response at least a day ago, but apparently it was lost.


I have no choice but to resort to a Dreaded ASCII Graphic bwahahahahaha!


Code:
    +---o  --1%
    |  /
    | /
    |/
    +
   /|
  / |
 /  |
o---+      --0%
^       ^
T=0s    T=Ns
Blue is the PID CV output; orange is the clamped, rounded valve position signal. To first order, the effect of the valve position will over the time period 0s to N seconds will proportional to the area under the curve over that time period i.e. 0.5N %-s. Without clamping and rounding, the effect of the CV if sent directly to the valve would be proportional to the same area.

Obviously there are a lot of unknowns, e.g. does the valve position match the signal, etc., etc., etc. But those are all second-order effects. Given the paucity of information, first-order guesses are the best we have; second-order minutiae are not worth pursuing.

Bottom line: yes, there is some small deadtime, but given the large time constant(s) of this system, a Td of 0 will not prevent a tuned system that meets OP's requirement of +/-0.05degC.
  Reply With Quote
Old February 24th, 2021, 12:23 PM   #126
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,356
Quote:
Originally Posted by drbitboy View Post
no, I thought I posted a response at least a day ago, but apparently it was lost.


I have no choice but to resort to a Dreaded ASCII Graphic bwahahahahaha!


Code:
    +---o  --1%
    |  /
    | /
    |/
    +
   /|
  / |
 /  |
o---+      --0%
^       ^
T=0s    T=Ns
Blue is the PID CV output;
orange is the clamped, rounded valve position signal. To first order, the effect of the valve position will over the time period 0s to N seconds will proportional to the area under the curve over that time period i.e. 0.5N %-s. Without clamping and rounding, the effect of the CV if sent directly to the valve would be proportional to the same area.

Obviously there are a lot of unknowns, e.g. does the valve position match the signal, etc., etc., etc. But those are all second-order effects. Given the paucity of information, first-order guesses are the best we have; second-order minutiae are not worth pursuing.

Bottom line: yes, there is some small deadtime, but given the large time constant(s) of this system, a Td of 0 will not prevent a tuned system that meets OP's requirement of +/-0.05degC.
I am talking about the original plots. There is huge dead time between the control signal to the valve and when the blue line, the temperature, response.


If you can't get this right there is no hope.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 24th, 2021, 01:22 PM   #127
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317
Quote:
Originally Posted by Peter Nachtwey View Post
I am talking about the original plots.
No, you are not ...

Quote:
Originally Posted by Peter Nachtwey View Post
The PV can never respond to a change in the CV that hasn't happened yet....
but that is a distraction.

Quote:
Originally Posted by Peter Nachtwey View Post
There is huge dead time between the control signal to the valve and when the blue line, the temperature, response.

Cf. Post #119: to my finely calibrated eyeball, from the dynamics of the orange and blue lines immediately after the white vertical bar it is impossible to identify lag vs. deadtime; even if the latter, it cannot be more than a quarter-hour, so please justify how that is called "huge," given the obvious size of the time constant.

Quote:
Originally Posted by Peter Nachtwey View Post
If you can't get this right there is no hope.
Are you sure you are not swapping Direct- vs. Reverse-acting?
  Reply With Quote
Old February 25th, 2021, 08:54 PM   #128
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: United Welfare States of America
Posts: 7,356
There is no hope or help until you figure out what dead time is.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon
  Reply With Quote
Old February 25th, 2021, 09:48 PM   #129
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317
Quote:
Originally Posted by Peter Nachtwey View Post
There is no hope or help until you figure out what dead time is.

I've known what deadtime is for over 40y. The question here is not if there is any deadtime in this process; of course there is. The question is whether it is significant enough to need to be compensated for via the PIDE parameters.

Last edited by drbitboy; February 25th, 2021 at 09:51 PM.
  Reply With Quote
Old February 26th, 2021, 09:08 AM   #130
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317



xxx.png
  Reply With Quote
Old February 26th, 2021, 02:56 PM   #131
GrizzlyC
Member
Canada

GrizzlyC is offline
 
Join Date: Feb 2021
Location: Alberta
Posts: 28
I have an updating on my tuning process.

After messing with a lot a parameters I found that (at least with the AB PIDE) that derivative control is not required for this process. A PI controller is all that is necessary. This is a graph over 24 hours with the following parameters.

Red = Setpoint (12C)

Upper Blue = Lower Temperature
Lower Blue = Lower Valve Position

Upper Purple = Upper Temperature
Lower Purple = Lower Valve Position

P = 60
I = 120
D = 0

My output is quite noisy but this it within acceptable levels. Keep in mind this small picture contains 2880 data points per pen line. One interesting thing I find across all my tanks is that the output of the valves roughly follows the temperature instead of lagging like it was before.

The next big test is to see how the PID or more effectively the PI reacts to a large temperature change and if it can predict adequately to not overshoot.

Your guys' input has been extremally valuable but i'm still open to suggestions on how to improve on this.
Attached Images
File Type: png Tank 15 P60 I120.PNG (26.0 KB, 69 views)
  Reply With Quote
Old February 26th, 2021, 03:02 PM   #132
GrizzlyC
Member
Canada

GrizzlyC is offline
 
Join Date: Feb 2021
Location: Alberta
Posts: 28
Here is another one over a 2 hour time period. Same parameters same pen legend.
Attached Images
File Type: png Tank 13 P60 I120.PNG (22.1 KB, 54 views)
  Reply With Quote
Old February 26th, 2021, 09:23 PM   #133
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 2,317
Quote:
Originally Posted by GrizzlyC View Post

P = 60
I = 120
D = 0


ne interesting thing I find across all my tanks is that the output of the valves roughly follows the temperature instead of lagging like it was before.
Yes, D is zero, and I is so large that integral action is minimal, so this is essentially a P-only controller.

Try P=50, I=60, as @Mispeld suggested.




Quote:
Originally Posted by GrizzlyC View Post
Upper Blue = Lower Temperature
Lower Blue = Lower Valve Position

Upper Purple = Upper Temperature
Lower Purple = Lower Valve Position

How can Lower Blue and Lower Purple be the same thing (Lower Valve Position)?


Is there more than one valve?


Are these actual valve position(s), or are they the post-processed (rounded, clamped) PID output CV signal sent to the valve(s)

Last edited by drbitboy; February 26th, 2021 at 09:26 PM.
  Reply With Quote
Old February 27th, 2021, 01:46 PM   #134
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 528
Quote:
Originally Posted by GrizzlyC View Post
Your guys' input has been extremally valuable but i'm still open to suggestions on how to improve on this.
Some of your (non-mutually-exclusive) options moving forward:

1. Continue trial-and-error tuning with limited information available. As noted, the second set of results now showing PV and CV in phase implies a shift from integral-dominant to proportional dominant. Improvement is likely possible within the current operating window of the CV.

2. Investigate and improve the control valve situation.

a) If the root cause of unreliable operation cannot be fixed, then consider a deadband-like algorithm on the CV output instead of the round-to-one-percent strategy.

b) Characterize the value flow at typical coolant operating pressure. Then linearize the flow vs. CV response with an inverse or stepwise compensation function after the PIDE.

3. Increase process understanding to guide incremental tuning decisions.

a) Run in manual at fixed output, as long as safety- and cost-wise possible, to get insight on the nature and source of process disturbances.

b) If step 3a demonstrates an inherently stable process (i.e., PV basically flatlines when CV flatlines), introduce a reasonable open-loop (manual mode) step change in the CV to observe PV response. This will take a lot of patience for the slow process, but can be a gold mine of information for modeling, simulation, and tuning under the assumption of little or no external influence during the step test.

c) Develop a first principle model for the process such as can be used in simulation and computational tuning techniques.

4. Install instrumentation to better understand the process and potential disturbances. For example, a flow/temperature device on the coolant supply line to measure flow linearity and source temperature stability under normal and test conditions. Keyence makes a clamp-on for flow and pipe temperature that should be fine with diluted glycol. (I have good experience with Keyence products, but their sales tactics not so much.)

5. Determine from the "process owner" the required control system performance. Additional action is a cost in time and possibly equipment. Does potential improvement in process yield justify more spending? This will give you a budget. There should be an objective goal to reach in terms of a control system performance measurement (e.g., error range, error std dev, integrated error).
__________________
"The greatest enemy of knowledge is not ignorance, it is the illusion of knowledge." -Stephen Hawking

Last edited by Mispeld; February 27th, 2021 at 01:50 PM.
  Reply With Quote
Old February 27th, 2021, 10:07 PM   #135
GrizzlyC
Member
Canada

GrizzlyC is offline
 
Join Date: Feb 2021
Location: Alberta
Posts: 28
Quote:
Originally Posted by drbitboy View Post

Try P=50, I=60, as @Mispeld suggested.

How can Lower Blue and Lower Purple be the same thing (Lower Valve Position)?

Is there more than one valve?

Are these actual valve position(s), or are they the post-processed (rounded, clamped) PID output CV signal sent to the valve(s)

Sorry that was a typeo it theres is an upper and lower jacket valve. I tried p 35 and I 60 and the reaction was still to slow. It seems that the higher the I the more reactive the CV, however this does also produce a lot of noise on PV change.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
NOP instruction foremanml LIVE PLC Questions And Answers 26 September 8th, 2014 04:40 PM
Sample Time of the PID ISA jcp LIVE PLC Questions And Answers 20 March 10th, 2012 02:29 AM
S7200 Siemens PID Control with dead time Espartaco LIVE PLC Questions And Answers 10 April 21st, 2011 06:18 AM
Cascading Sparky LIVE PLC Questions And Answers 24 February 17th, 2003 12:33 PM
Trying to find a website ganutenator LIVE PLC Questions And Answers 9 January 5th, 2003 04:06 PM


All times are GMT -5. The time now is 06:26 PM.


.