Hello frnds
I have power flex 70 drive , i fill all the parameters but orange light blinks contineously . Please help me .
According to the mannual parameter 214 is wrong.
Plz tell me what to fill
 
If possible, post the message on the drive's HIM module (if it is equipped with one). My guess is that it says "Stop Asserted".

If possible, post the value of Parameter 214 (Start Inhibits) and Parameter 288 (Stop Owner).

Is the drive connected to a PLC over a network (Ethernet, ControlNet, DeviceNet), or controlled via hard-wired inputs like pushbuttons and selector switches ?

In general, the direction of a PowerFlex 70 drive is selected by a discrete input, by a selector on the HIM module, or by a bit in the drive's networked Command word. It can also be determined the polarity of the reference signal if the speed reference is configured for "Bipolar" (Parameter 190).

The more you can tell the Forum community about your application, the better we can assist you in understanding the configuration of the PowerFlex 70 drive.
 

Similar Topics

Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
Replies
0
Views
44
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
85
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
Replies
3
Views
159
i have a flashing yellow sts light. "Stop Asserted" message on one of my PF 753"s, but no bits set in parameter 961. The safety circuit tests...
Replies
1
Views
189
hello everyone. I have a 525 VFD that works, the screen shows the output voltage and the output frequency but in UVW I do not have voltage...
Replies
0
Views
170
Back
Top Bottom