S7-200 recognition problem

ibora

Lifetime Supporting Member
Join Date
Dec 2008
Location
Izmir
Posts
66
Hi everyone,
I'm trying to connect a s7 224 cpu over ppi. I'm establishing connection but microwin shows plc as unknown. If anyone knows solution pls help me. Please look up to the attached picture.

20180829_211656.jpg
 
What is the part number? If it is an S7-200 CN or S7-200 smart, those are more or less China only products and regular microwin more or less doesn't support them.
 
Thank You for answer mk42,
I'm sure it's not China product. But to be sure what is the part number exactly i have to check on site tomorrow.
 
The addresses look a bit wonky, Microwin normally takes address 0 and the PLC addresses after that. Maybe try setting the Microwin address back to 0 in Communications / Set PG/PC Interface / PC PPI cable. And make sure you allow it to search all baud rates.
 
Thanks for all answers,
Yes, i tried to make microwin adress zero but when i try to connect again its turning to 2. I didn't understand why. But tried many times result is same.
 
Where did you get the PPI cable from? I have found that some of the slower cheaper cables will return unknown but they will still work

Have you tried to upload the program? what is the part number of the cable?
 
Try going up to 19,2

You will need to change the speed in the program and download it to the CPU then change your cable to match and then try it again

Make sure you backup the program before you make any changes also dont go faster then 19,2 as that cable I think is limited
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
61
Hi folk, I would like to know what kind of Parameters should I setup for controlling with Profibus. My old Lenze 8200 motec 0.25kW have a busted...
Replies
0
Views
61
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
Replies
4
Views
114
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
87
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
72
Back
Top Bottom