Servo positions not updating.Could you please explain this code ?
Rob S.
Sep 2008
Maryland
739
Good Afternoon ,
We have a new machine from Italy , and for some reason , the servo actual positions quit updating on the HMI. I looked at the tag in the "connection" tab in Numeric Display and it is
{[CLX]HMI.Scope.Recipe_Par[153]}.
I thought it was going to be simple , till I looked at the code below. I
know it not the easiest to read , the way I have it. What do you think the S:FS Bit stands for in a ControlLogix ? It may be that this bit is not true. Where would I see this. Also attached is another piece of code , that a cross reference of that HMI tag showed ?
What is a SIZE instruction used for ?
Thank you so much for your help. Why is code written so difficult sometimes :( ?
// Inizializzazione parametri all'accensione
// The below program initialises data to desired power up values. This only runs on S:FS Bit.
IF S:FS THEN
MAN_AX_LAST :=32;
// Tutti i parametri di ricetta invisibili
// All recipe parameters Not Displayed
FOR INDEX:=0 TO (MAX_MACHINE_PARAMETERS_NR-1) BY 1 DO
HMI_CONFIG.RECIPE_PAR_MIN_VALUE[INDEX] := 0;
HMI_CONFIG.RECIPE_PAR_MAX_VALUE[INDEX] := 0;
HMI.SCOPE.RECIPE_PAR[INDEX] := 0;
END_FOR;
Rob:
This info comes from help :
Size:
This information applies to the CompactLogix 5370, ControlLogix 5570, Compact GuardLogix 5370, GuardLogix 5570, CompactLogix 5380, CompactLogix 5480, and ControlLogix 5580 controllers.
The SIZE instruction finds the size of a dimension of an array. This instruction can also operate on a string where it returns the size of the DATA portion of the string.
I have never worked with ControlLogix, but something tells me it could be a System:First Scan? That makes sense as the code inside of the IF structure seems to do some initializations.
Thanks for your thoughts and information. Where would I find this S:FS bit in the program . I recall seeing something similar in RS Logix 500 ( SLC ) in the controller folder . I will check online today , and see if it is in the processor folder. If that is a condition to make those positions update , is it a bit I can force ?.
Thanks again
No S:FS can not be forced.
If you want to check it just modify your program to make s:fs to add 1 to a number you know is constant.
Every time you restart your plc that number will add 1 to itself.
The S:FS bit is just being used to clear out the recipe when the PLC is first powered up. This will stop the end used from running whatever recipe was loaded when the PLC was last powered up. So if for example, Bubba doesn't want to look for the real problem and tried the great cure all of cycling power to the processor, the program will force you to reselect the recipe you want to use. Elsewhere in the code are the instructions for selecting what recipe to load into memory.
Bubba.
Hi People, I've had a two servos working in tandem for about 2 years now and the company say they are not happy about having to reteach them...
2,124
Hi, I'm working on Mitsubishi MR-J5-70A amplifier, and need some advice on selecting fuse size. Main power is 1ph 240VAC, and in the manual, it...
65
Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
93
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
92
Hi all, I am having a machine with old 802d sl siemens controller. I am trying to tune servo by Siemens starter software. Anyone experienced...
69
