OkiePC
Lifetime Supporting Member
YES! Today, after I put the 160 series drive in was the first time it faulted while I had the DC Bus volts on the display.
I had just set AUTO RETRIES = 3, DELAY = 3.0 . . .
So I got to see the DC Bus go from 740-somthin' back down to 630 over a period of about 3 seconds.
The other two times it faulted while I was staring at it (with the PF40 yesterday) it did fault with no run command (it was enabled).
Same problem, new drive, but I saw what looked like serious regeneration.
It was the meat that was missing.
When I tried to make it fault with a rapid decel ramp, I wasn't putting enough meat on the belt. When the inspection operator runs the system in full auto, there is probably 500 more pounds of meat on this belt! Doh!
So I wish I had thought of it while I was at work, but first thing in the a.m.:
1) Try coast stop.
2) If stop distance is insufficient, experiment with DC injection braking.
3) If #2 proves successful, monitor Heatsink temp and motor temp.
4) Order DB and 1 Pole OL relay.
Yes, I am thinking I'll put a DB on it no matter what, and I gotta get us a working scope. I could have ordered the solution yesterday if I had the right tools.
And two more drives are going in this MCC soon. (2 x 7.5HP) and they all need devicenet, so I can chart DC Bus easily and identify regeneration.
Thanks again...and I'll try to update what happens tomorrow.
I had just set AUTO RETRIES = 3, DELAY = 3.0 . . .
So I got to see the DC Bus go from 740-somthin' back down to 630 over a period of about 3 seconds.
The other two times it faulted while I was staring at it (with the PF40 yesterday) it did fault with no run command (it was enabled).
Same problem, new drive, but I saw what looked like serious regeneration.
It was the meat that was missing.
When I tried to make it fault with a rapid decel ramp, I wasn't putting enough meat on the belt. When the inspection operator runs the system in full auto, there is probably 500 more pounds of meat on this belt! Doh!
So I wish I had thought of it while I was at work, but first thing in the a.m.:
1) Try coast stop.
2) If stop distance is insufficient, experiment with DC injection braking.
3) If #2 proves successful, monitor Heatsink temp and motor temp.
4) Order DB and 1 Pole OL relay.
Yes, I am thinking I'll put a DB on it no matter what, and I gotta get us a working scope. I could have ordered the solution yesterday if I had the right tools.
And two more drives are going in this MCC soon. (2 x 7.5HP) and they all need devicenet, so I can chart DC Bus easily and identify regeneration.
Thanks again...and I'll try to update what happens tomorrow.