ML1200COMMUNICATION
thank rsdoran
i found your information is very useful
as ml 1200 communication port (com0)is not blinking means not configured as DH485,may be an other configuration may be rs232 .
there is allen bradley usb to serial adapter
(9300-USBS ),.
I WOULD LIKE TO ASK IF IHAVE THIS ADAPTER CAN I USE IT WITHOUT INTERFACE CONVEROR OR NO ?
I YES WHAT IS THE CONFIFURATION AND PROTOCOL .
THANK YOU VERY MUCH

Someone please offer more assistance.
 
🤷

Ron, I suffer from CRS-II. What I can't remember, I make up as I go along...

In the first attached PDF file, it appears that the 9300-USBS Adapter only converts from a computer USB port to a Serial (RS232) port, and it does not also convert from RS232 to RS485, so you will need another adapter to do that. The traditional one for Allen-Bradley SLC's was the 1747-PIC (Personal Computer Interface Card), but nowdays you need the 1747-UIC.
 