Versamax CPU001 RS485 RTU

alencknovi

Member
Join Date
Jun 2019
Location
Croatia
Posts
7
I want to communicate with versamax CPU001 on port 2 with rtu slave.
I build up a cable two wire as per instruction here:(typical 2 wire)
http://technolink.spb.ru/downloads/GE_Intelligent_Platforms_PROFICY/documents/Modbus_GFK2220C.pdf

And have 485 to ethernet converter that has 2 wire connection.
On controller i have set up port RTU only 19600, 2 wire

I am trying to send commands but i get no response from plc at all.
Dont know what where to look for mistake or should i have something in ladder to initiate communication when using plc as slave?
 
Make sure your polarity is correct between the PLC and your converter. GE's pin labeling can be a bit confusing. "A" on the GE side is minus. "B" is plus.
You don't need any ladder logic in the PLC when the port is set up as a slave.
 

Similar Topics

Temporary lost power to plant .. One of the processor fault when power were restored.. I cleared fault, but all of the Inputs to the I/O module...
Replies
1
Views
1,671
egcp-2 from woodward has rs422 port which can be used for modbus communication and gefanuc versamax plc has rs485 port which supports modbus...
Replies
0
Views
3,167
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
194
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
131
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
Replies
4
Views
387
Back
Top Bottom