siemens micromaster 440

kulmaint

Member
Join Date
Dec 2018
Location
AUSTRALIA
Posts
42
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with
mm440. all parameters are crosschecked. please help to resolve the issue.
 
Trace the current and torque.
When you complete that, how does that compare to nameplate data.
Reply back with screenshots
 
It might be due to the fact that the 420 was not capable of Sensorless Vector Control and the 440 is, so if you have selected SVC but have not performed an auto tune procedure, the drive is using incomplete information for the motor equivalent circuit and likely overfluxing the motor.
 
It might be due to the fact that the 420 was not capable of Sensorless Vector Control and the 440 is, so if you have selected SVC but have not performed an auto tune procedure, the drive is using incomplete information for the motor equivalent circuit and likely overfluxing the motor.

All a guess since he said he “cross checked “ all the parameters
 

Similar Topics

My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
Replies
4
Views
2,960
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0). I'm...
Replies
1
Views
3,036
I am trying, for the first time, to write values to the control word of a Micromaster 440 using an S7-300 PLC. I barely know what I'm doing, and...
Replies
4
Views
2,566
Hello good day : micromaster have a 440 installed on a machine, when I push button start machine micromaster machine works well, up to speed and...
Replies
3
Views
2,153
Hi All, Today we had a drive die on us. There was no backup but we have a duplicate drive in service. Can't upload via AOP or starter but Siemens...
Replies
11
Views
11,391
Back
Top Bottom