Derivative using a PID Loop
power_guy
Jan 2004
I am using a GE90/70 PLC.
Is there a way to use a PID loop to take the derivative of a temperature. If the temperature increase is more than 31.6 F per minute then the ouput pid would increase?
Wow, you've got some unique ideas about using PID!
When you say "take the derivative of a temperature", do you mean calculating the rate of change of the temperature with time (dT/dt)? If so, it's far easier to just do the arithmetic than try to extract the derivative from the PID equation.
Set up a self-resetting timer or a timed interrupt at any convenient time increment. Calculate the difference between the current temperature value and the stored value from the last time you did the calculation. Divide that difference by the time increment to get the rate of change, and copy the current temperature value to the storage location.
analog PID work with very small deviation.
so if you want something if over a border then you will have to make your own program.
If you want to look for sharp peaks in small time you can use two samples and the time in between. calculate minuteraise by 60000/looptime*deviation.
if you want to have average you will have to take a lot of samples and check every minute if average is climbing to much.
So, I have a problem.. Maybe. I only had 3 test runs with the system so I'm not sure. It is a steam cooling system, and I thought it would be...
2,094
This might seem like a dumb question however I can't see the difference and can't test it as I don't have an allen bradley PLC available. In the...
25
10,467
Hi, I have a ControlLogix processor and I'm using RSLogix 5k V19. I am trying to find the derivative or the rate of change of a signal every...
2,937
In my very limited experience with control loop tuning, I found the use of derivative to be a hindrance, and dialed in quarter decay with...
4,588
I cannot see a derivative function built into RSLOGIX 5000 v16. I only see an integrator. I wish to estimate the rate of change of a signal with...
6,074