Does Inhibiting a module stops the scanner from scanning
Hello guys,
We a compact logix processor and one of the safety input modules 1734-IBS seems to be faulty as sometimes the module led turns red which causes a network fault. The inputs of the module are not used. Can I inhibit the module? Will it still cause the scanner to go in fault |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2015
Location: Yokohama
Posts: 1,386
|
Hello:
Do you want to prevent the processor from faulting? |
![]() |
![]() |
#3 |
Member
|
I don't think you can disable any safety module
the communications to safety modules is handled differently the standard modules if the communication is lost the safety controler will fault and turn off the safety controls Think about it if a monitored safety input were to fai would you reall want the equipment to just keep running and hurt somebody |
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2015
Location: Yokohama
Posts: 1,386
|
GaryS, I think you are right and I am wrong. The screenshot above is for a non-safety device. I just checked, the same screen for a safety device has the option "Major Fault On Controller..." greyed out.
To bornwild's answer, it should be possible to inhibit the safety device. Not sure if the fault in the PLC will not be genrated again once you clear the fault. |
![]() |
![]() |
#5 | |
Member
![]() ![]() Join Date: Jul 2015
Location: MKE
Posts: 38
|
Quote:
"ID: PN1590 Product Notice 2022-05-001 - Allen-Bradley POINT Guard I/O 1734-IB8S/B, 1734-IB8SK/B Intermittent Connection Fault" |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Module 1756-M02AE Rev.3.8 Fault | Tim ODell | LIVE PLC Questions And Answers | 4 | September 3rd, 2017 06:20 PM |
Barcode scanner communication with 1756-ENBT module | haribaburam | LIVE PLC Questions And Answers | 6 | August 1st, 2017 04:37 PM |
AS interface master scanner module faults clx | kf5pv | LIVE PLC Questions And Answers | 7 | July 14th, 2010 04:47 AM |
AB 1746-HS module - IMC 110 motion controller | raj | LIVE PLC Questions And Answers | 12 | February 20th, 2009 01:36 AM |
SLC 5/03 data loss | andydaoust | LIVE PLC Questions And Answers | 1 | October 10th, 2002 07:38 PM |