Old November 23rd, 2022, 05:03 AM   #1
bornwild
Member
Saudi Arabia

bornwild is offline
 
Join Date: May 2010
Location: Riyadh
Posts: 429
Does Inhibiting a module stops the scanner from scanning

Hello guys,

We a compact logix processor and one of the safety input modules 1734-IBS seems to be faulty as sometimes the module led turns red which causes a network fault. The inputs of the module are not used. Can I inhibit the module? Will it still cause the scanner to go in fault
  Reply With Quote
Old November 23rd, 2022, 07:21 PM   #2
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 1,386
Hello:
Do you want to prevent the processor from faulting?
Attached Images
File Type: png 2022-11-24_.png (77.7 KB, 42 views)
  Reply With Quote
Old November 23rd, 2022, 10:31 PM   #3
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,910
I don't think you can disable any safety module
the communications to safety modules is handled differently the standard modules
if the communication is lost the safety controler will fault and turn off the safety controls
Think about it if a monitored safety input were to fai would you reall want the equipment to just keep running and hurt somebody
  Reply With Quote
Old November 24th, 2022, 02:31 AM   #4
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 1,386
GaryS, I think you are right and I am wrong. The screenshot above is for a non-safety device. I just checked, the same screen for a safety device has the option "Major Fault On Controller..." greyed out.


To bornwild's answer, it should be possible to inhibit the safety device. Not sure if the fault in the PLC will not be genrated again once you clear the fault.
  Reply With Quote
Old November 24th, 2022, 11:42 AM   #5
glennz
Member
United States

glennz is offline
 
Join Date: Jul 2015
Location: MKE
Posts: 38
Quote:
Originally Posted by bornwild View Post
Hello guys,

We a compact logix processor and one of the safety input modules 1734-IBS seems to be faulty as sometimes the module led turns red which causes a network fault. The inputs of the module are not used. Can I inhibit the module? Will it still cause the scanner to go in fault
Be aware of this from the Knowledgebase as you work on that problem:

"ID: PN1590 Product Notice 2022-05-001 - Allen-Bradley POINT Guard I/O 1734-IB8S/B, 1734-IB8SK/B Intermittent Connection Fault"
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Module 1756-M02AE Rev.3.8 Fault Tim ODell LIVE PLC Questions And Answers 4 September 3rd, 2017 06:20 PM
Barcode scanner communication with 1756-ENBT module haribaburam LIVE PLC Questions And Answers 6 August 1st, 2017 04:37 PM
AS interface master scanner module faults clx kf5pv LIVE PLC Questions And Answers 7 July 14th, 2010 04:47 AM
AB 1746-HS module - IMC 110 motion controller raj LIVE PLC Questions And Answers 12 February 20th, 2009 01:36 AM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 07:38 PM


All times are GMT -4. The time now is 05:00 PM.


.