Problems Connecting to Micrologix via Ethernet
Good morning,
I have a bizarre issue with connecting directly to a Micrologix 1400 via ethernet. It recently popped up on a service call when connecting directly to the plc, I could not ping it and could not see it in rslinx. Everything was what it should be as far as my ip and subnet. I ended up connecting using DF-1. When I got back to the office I tried one on the test bench and had the same result. Some interesting things are: After attempting the Micrologix connection if I disconnect my ethernet cable and plug it into a compactlogix I can ping and see the compactlogix, then I disconnect from the Compact and plug back into the Micrologix I then can see and ping the micrologix. Very weird. Also, if the micrologix is connected to a switch all is well. I've never had an issue connecting directly to a Micrologix. Has anyone else experienced this issue and/or have any suggestions to fix it? Thanks for the responses. |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Jan 2011
Location: NC
Posts: 1,232
|
Try a cross over cable instead of a patch cable.
|
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Nov 2017
Location: Michigan
Posts: 29
|
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Nov 2017
Location: Michigan
Posts: 29
|
The crossover cable did not work. I cannot communicate with a micrologix or compactlogix. Any other suggestions?
|
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Jan 2011
Location: NC
Posts: 1,232
|
Ethernet port on the Laptop is going bad or bent pin on laptop port. Sometimes works sometimes don't. Do you have a USB to Ethernet adaptor? We have used the StarTech.com Part#USB31000S and they work well for quickly adding an Ethernet port.
|
![]() |
![]() |
#6 | |
Member
![]() ![]() Join Date: Nov 2017
Location: Michigan
Posts: 29
|
===solved===
Quote:
Thanks again. |
|
![]() |
![]() |
#7 | |
Lifetime Supporting Member + Moderator
|
Quote:
This isn't usually necessary (and it is a Windows thing, not a Rockwell thing) but it can't hurt to try. |
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Nov 2022
Location: Chihuahua
Posts: 2
|
Similar problem
Hey there, i have a similar problem with one client, I have a Micrologix 1400. I can conect to it via DH-485. but i cant connect via ethernet.
*My Laptop have the IP 192.9.150.253 *PLC have 192.9.150.51 *I CAN ping PLC with Laptop (4 packages send, and 4 packages recived) *I CANT see my ethernet adapter is connected to something *Ethernet IP Driver on RS Linx using my ethernet adaptor dont find anything *Ethernet Devices Driver on RS Linx using my ethernet adaptor dont find anything *I did the same test with 2 different Laptops *I can see other Micrologix 1400 and compact logix in the ethernet Network in the 2 Lap Tops where i was testing. *I connected an USB to Ethernet Converter, and is working on PC, but cant see the PLC in RSLinx, but i can ping the PLC with that Converter to PLC for mee it seem port ethernet is damaged. questions: *Is something that i can do to fix that? *Can i use somehow DH-485 port with some ethernet converter to add that micrologix to the network? (it have some connections with 1 HMI and 1 Compact Logix) *Or i have to buy a new PLC? TYVM in advance for your time to look in to this problem Last edited by Adesdrac; November 24th, 2022 at 02:39 PM. |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 715
|
Try a different cable. Believe it or not, I chased down an issue where I could ping it but RSLinx/RSLogix wouldn't talk to it. I swapped the cable and it started working. That was my last ditch "hail Mary" thing to try after a LONG time banging on it, so I ended up cutting the end off of the cable so I didn't get bitten again (in that shop, it wasn't unusual for stuff that had been thrown away to find its way back into a stash somewhere, so we got in the habit of breaking things enough they couldn't even be attempted...).
|
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Nov 2022
Location: Chihuahua
Posts: 2
|
Ty, I tryed that, I buyed a New ethernet cable, no luck, then I made a New one, But no luck. I guess in this case is the port is damaged
Last edited by Adesdrac; December 1st, 2022 at 12:14 PM. |
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 715
|
I wonder also if the port is set to auto-negotiate its speed (if that's an option on that ML). It could be that plugging into the CompactLogix with auto-negotiate enabled sets it up to work. Could be something to look at.
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Connecting PLC to muliple PC via ethernet | macstorm | LIVE PLC Questions And Answers | 1 | January 28th, 2016 10:34 PM |
Messaging over Ethernet between MicroLogix1500/NET-ENI and CompactLogix | davidwarrenabaxis | LIVE PLC Questions And Answers | 6 | January 25th, 2016 12:23 PM |
MicroLogix to Powerflex 525 via Ethernet | lam2363 | LIVE PLC Questions And Answers | 7 | December 28th, 2015 03:35 PM |
Micrologix 1400 Ethernet Port?? | Coops | LIVE PLC Questions And Answers | 1 | April 21st, 2011 06:03 AM |
Micrologix 1100 can't comminucate with Panelview Plus 600 through ethernet | plemonse | LIVE PLC Questions And Answers | 2 | December 27th, 2010 12:49 PM |