I have a question, should you use fuses for all your outputs including analog? Also how should you size your fuses , just based off of your wattage from your device? I wasn't sure if there where fuse sizing standards like you would find in the NEC? Does the NEC have a specific artlicel pertaining to control wires?

My next question is when should you pull a shield belden cable? Would this be mainly for analog controls or precision instrumentation? Thanks in advance
 
Can't speak for the NEC as I haven't worked in it's jurisdiction, fuses are rated in amps so make sure you get the right voltage for the circuit. E.g. I install 24V DIN Rail UPS' and the fuse is rated at 25A 32V, specified in the datasheet.

As for Belden, I use it for comms such as Modbus RTU on 2 wire (with shield/screen S/STP) RS485 circuits. CY cable is fine for 4-20mA, screen connected at one end only.
 

Similar Topics

To quickly test a plc output which is wired to a relay do I dob a cable between the output and 24vdc+ source I.e something with 24vdc+ live such...
Replies
6
Views
692
I have a love hate relationship with LED status lights. I like them because they last a long time...BUT... They have a problem with PLC outputs...
Replies
4
Views
853
Engineers and designers, question. Do you typically fuse the PLC outputs ? I see some that are fused and many that are not. I typically fuse...
Replies
3
Views
1,061
Hi group! Repeatedly found answers to some questions in the PLC's programming world, now I decided to ask the question directly) Now I am...
Replies
22
Views
4,228
Hello Everyone! I've Mitsubishi FX2N-80MR PLC. It has relay type 40 outputs. I need one PWM output and two Pulse outputs for servo and stepper...
Replies
1
Views
1,454
Back
Top Bottom