Rockwell 1734-ie2c problem

buoanventura

Member
Join Date
Jun 2011
Location
italy
Posts
5
Hi Guys,

We Have some problem with 1734-ie2c module with controllogix cpu, sometimes the input value went to 0 without Module alarm.
suggestions? 🤞🏻
 
What type of error are you expecting? I would check the configuration. You're probably set for 0-20ma instead of 4-20ma. (Assuming you're anticipating an out of range error)
 