I need to develop logic for controlling the flow through 8 media filters with a Siemens S7. The flow will be divided by the total number of filters that are online. That is the easy part. A PID will monitor the effluent flow from each individual filter and modulate the effluent valve.

Where I am running into trouble is with the development of a "flow trim" based on filter performance. This Trip will be 10-20% of the control loop.

The idea is for filters with higher turbidity to receive less flow and the filters with the lowest will see more flow.

So for example:

(Max allowable flow through any given filter = 1MGD)

Filter 1 Turbidity 0.08 -> Eff Flow 1.00 MGD
Fitler 7 Turbidity 0.10 -> Eff Flow 0.95 MGD
Filter 5 Turbidity 0.15 -> Eff Flow 0.90 MGD
Filter 2 Turbidity 0.20 -> Eff Flow 0.85 MGD
Fitler 4 Turbidity 0.20 -> Eff Flow 0.80 MGD
Filter 3 Turbidity 0.25 -> Eff Flow 0.75 MGD
Fitler 6 Turbidity 0.27 -> Eff Flow 0.65 MGD
Filter 8 Turbidity 0.30 -> Eff Flow 0.60 MGD
......

Let me know if you have any ideas or need me to clarify. Thanks!
 
Last edited:

Similar Topics

I have 14 assembly lines and an LED display with a siren looking light and a list of 18 tunes. There are 3 cells (each cell is 4-5 assembly...
Replies
3
Views
2,093
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
47
When supplying variable frequency drives (vfd), should we install the line filter (emc) before the reactor (choke), or reactor before filter...
Replies
2
Views
191
Hi. I'd like to have a filter on an Alarm Summary page where I could pick which of the 3 groups I created I want to display on the screen. I...
Replies
3
Views
542
Good morning, I'm new to PLC and HMIs, and I was given the following problem: I need to be able to filter alarms and events that are only related...
Replies
0
Views
387
Back
Top Bottom