jthyge Member J Join Date Feb 2020 Location Randers Posts 10 Feb 27, 2020 #1 Hello Is there any way to communicate with a CompactLogix L30ER with plain TCP / IP. Similar with the TCON in Siemens TIA Portal? I need to communicate with at S7-1200 in TCP / IP. And have a working solution for the Siemens PLC.
Hello Is there any way to communicate with a CompactLogix L30ER with plain TCP / IP. Similar with the TCON in Siemens TIA Portal? I need to communicate with at S7-1200 in TCP / IP. And have a working solution for the Siemens PLC.
AlfredoQuintero Lifetime Supporting Member A Join Date Feb 2015 Location Yokohama Posts 1,545 Feb 27, 2020 #2 Would this information be useful for you? Application technique, EtherNet/IP Socket Interface https://literature.rockwellautomation.com/idc/groups/literature/documents/at/enet-at002_-en-p.pdf
Would this information be useful for you? Application technique, EtherNet/IP Socket Interface https://literature.rockwellautomation.com/idc/groups/literature/documents/at/enet-at002_-en-p.pdf
widelto Member Join Date Jul 2005 Location Barranquilla, Colombia Posts 3,392 Feb 27, 2020 #3 @jthyge: Siemens has an application to communicate a S7 with compact/Controllogix. https://support.industry.siemens.co...ol-system-(clx-glx-controller)?dti=0&lc=en-AT
@jthyge: Siemens has an application to communicate a S7 with compact/Controllogix. https://support.industry.siemens.co...ol-system-(clx-glx-controller)?dti=0&lc=en-AT
Firejo Member Join Date Jun 2008 Location Redmond, WA Posts 1,507 Feb 27, 2020 #4 https://www.spectrumcontrols.com/products/universal-gateway/ A whole lot simpler than trying to deploy the Rockwell code
https://www.spectrumcontrols.com/products/universal-gateway/ A whole lot simpler than trying to deploy the Rockwell code
Masbeng Member M Join Date Feb 2020 Location Surabaya Posts 1 Feb 27, 2020 #5 How to connect vb6 winsock with PLC cj2m
Firejo Member Join Date Jun 2008 Location Redmond, WA Posts 1,507 Feb 28, 2020 #6 Masbeng said: How to connect vb6 winsock with PLC cj2m Click to expand... One, not even close to enough detail in your question, two, you're high jacking someone else's post. You should create a new post for your question.
Masbeng said: How to connect vb6 winsock with PLC cj2m Click to expand... One, not even close to enough detail in your question, two, you're high jacking someone else's post. You should create a new post for your question.
jthyge Member OP J Join Date Feb 2020 Location Randers Posts 10 Mar 1, 2020 #7 Hello. Thanks for your answers. Firejo->Im working on af school project, so cant buy hardware. I am now trying to crack the "EtherNet/IP Socket Interface".. Not easy. I have created at working socket, but in my "OpenConnection" MSG i get the error code 16#0005;Class or instance not supported. I have checked the FW. Its version 32.011, so this should be fine. The error code description does not help me much. Pictures: https://ibb.co/Fg4GHF7 https://ibb.co/fS9Z1Hf Last edited: Mar 1, 2020
Hello. Thanks for your answers. Firejo->Im working on af school project, so cant buy hardware. I am now trying to crack the "EtherNet/IP Socket Interface".. Not easy. I have created at working socket, but in my "OpenConnection" MSG i get the error code 16#0005;Class or instance not supported. I have checked the FW. Its version 32.011, so this should be fine. The error code description does not help me much. Pictures: https://ibb.co/Fg4GHF7 https://ibb.co/fS9Z1Hf
jthyge Member OP J Join Date Feb 2020 Location Randers Posts 10 Mar 7, 2020 #8 After hours of trying, and trying... It now works with the SIEMENS T_COMM FB. https://support.industry.siemens.co...ol-system-(clx-glx-controller)?dti=0&lc=en-AT But there is a fault in the documentation. With a S7-1200 CPU the InterfaceId is 64, not 1, as written in the documentation. Thanks for your answers.
After hours of trying, and trying... It now works with the SIEMENS T_COMM FB. https://support.industry.siemens.co...ol-system-(clx-glx-controller)?dti=0&lc=en-AT But there is a fault in the documentation. With a S7-1200 CPU the InterfaceId is 64, not 1, as written in the documentation. Thanks for your answers.