I'm talking to 6 altivar 312 drives and 2 212 drives via modbus out of the modbus port of an M340.

I'm sending speed commands to the drives.

I would like to read additional drive data during the process, but I need to not slow down the writes.

I've partially sped this up by only sending speed changes when the sp changes.

I haven't done much w/ error checking to ensure that the drive received the change correctly.

Was thinking of creating some sort of read/write var function where I could give different data requests being passed into the function different priorities.

Anyone ever do anything like this?
 
Redlion has a feature like this - called 'favor UI writes' or something like that. I implemented your concept in a Unitronics system a while ago that did the same - it had some standard reads in a rapid cyclic sequence (ModbusTCP but it doesn't matter from a logic standpoint) but if a write (arbitrary, think higher priority) was scheduled, it became next up in the sequence to execute and bumped the reads out - did not delete it, only inserted the write into the current sequence.

Are you using a single block (i.e. one write_var block) and swapping the data in and out or separate blocks, so one write_var for each of the eight devices? I think you could implement the prioritization logic either way.
 
Redlion has a feature like this - called 'favor UI writes' or something like that. I implemented your concept in a Unitronics system a while ago that did the same - it had some standard reads in a rapid cyclic sequence (ModbusTCP but it doesn't matter from a logic standpoint) but if a write (arbitrary, think higher priority) was scheduled, it became next up in the sequence to execute and bumped the reads out - did not delete it, only inserted the write into the current sequence.

Are you using a single block (i.e. one write_var block) and swapping the data in and out or separate blocks, so one write_var for each of the eight devices? I think you could implement the prioritization logic either way.

I am willing pay you or you and others to write this for me
 

Similar Topics

Hello all. I am trying to read out the values from a Carlo Gavazzi EM340 energy analyzer via Modbus communication. The S7-1200 PLC has the CB1241...
Replies
29
Views
3,638
I am trying to control a Rockwell Powerflex 525 via Modbus RTU (RS485) using an ABB AC800M DCS controller, and am having some issues getting...
Replies
2
Views
493
Been trying for a while to get a flowmeter with Modbus RS485 comms to talk to my Redlion Graphite HMI. Cable has been checked 3 times all good...
Replies
3
Views
832
Our main testing HMI has 2 Ethernet sockets in it. One is setup on IP address 192.168.30.99 and communicates with our main PC network...
Replies
1
Views
730
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
Replies
1
Views
1,138
Back
Top Bottom