ceilingwalker
Lifetime Supporting Member
Hello all. I have a customer that wants to make sure I use an isolation XFMR for the AC power going to a CLX processor. He wants to make sure that a spike seen on the line is not carried to the processor. I always use a step-down then a filter to accomplish this, not saying I am right but it makes sense to me. Thinking back to many years ago, I believe an isolation transformer is nothing more than a XFMR with a windings ratio of 1, uncoupling the load side electronically from the line side? The nature of all XFMR's is inherently isolation (except for autotransformers) anyway, including step-downs, correct? I have been searching for an isolation transformer that steps down from 480 to 120 but nothing with the word "isolation" stands out. All the isolation transformers I see have the turns ratio of 1. Any advice I could get as to the best way to accomplish this would be greatly appreciated.....and a way to explain this to the customer. Thank you