Hi... I'm working on a project where we are modifying an existing system. We are adding a 1756-ib32 input card to a spare slot on a existing rack. As the card is brand new the version number is 3.006. The processor is at rs logix 5000 v10. I have added the input card to the hardware configuration and downloaded to the plc. When online it shows the new module in fault with the following error message: (code 16#0317) Connection request error. Connection not scheduled. Rs logix will only let me assign version 2.1 for the input card (this is what makes me think it isn't compatible) so I changed the setup to disable the electronic keying of the new input card but still no joy.

Hope this makes sense to some of you and any information would be appreciated!

Thanks
 
You should be using RSNetworx for ControlNet to setup any device on the ControlNet network.

In the main rack should be a 1756-CNB controlnet card, which when you look at the properties tab, there is an RSNetWorx tab, which should point to a configuration file (.xc), with which you can view and edit the devices on the network, of which your new module has become an addition that needs to be added to the config file...

So you will require a copy of RSNetworx for Controlnet..
 

Similar Topics

Hi all. I'm having a hard time figuring out which cable goes with which module from Rockwell documentation, and my local Rockwell representative...
Replies
4
Views
830
Hi Guys, Here I have started to work on some difficult task, I hope I will get solution here. we have ABB CI-840 Master IO Module needs to be...
Replies
0
Views
597
Hi Guys, Here I have Started to work on some difficult task I hope I will get some solution here. I wanted to communicate ABB CI 840 IO Master...
Replies
0
Views
574
I have a spec that requires cable redundancy whether or not it makes sense. Also, I have to have redundant Processor Chassis where only one is...
Replies
9
Views
3,183
Hi Guys.... I am facing one issue. PLC Controller i.e. 1756-L74 is now showing the error as T03:C16 IO connection Failure.... What can be reason...
Replies
1
Views
1,588
Back
Top Bottom