Need some quick assistance out there. Right at this moment we have an old Modicon PLC. There is a remote I/O rack that is powered by a P810 power supply. There is an overload light on the power supply that is lit and the main processor shows a comm error. Does anyone know what this overload error means. We are going to try swapping out the power supply right now, but I am wondering is there something else we should try or do?

Russ
 
That was it

Well, the power supply was indeed the problem. I do have another question though. After reading the manual for the new power supply, I get the idea that if the power supply is not cause cause of the problem, that one of the I/O racks must have a short of some sorts. Is there any logical way to isolate that card other than to pull them all one at a time?
 
No, unless there are other symptoms. You will have to pull cards and disconnect racks until the problem is located (or remove everything and reinstall them one at a time).

Do you have multiple racks on the supply? Maybe one of the interconnect cables is bad?
 
The ploblem is a fail in the power supply, there are two capacitors together that have a shortcircuit you need to replace the values are 220uf 30v are locate next to sink transistors. good luck.
 

Similar Topics

Hi, I have a customer with an ancient modicon plc that is not going into run mode, Gould Micro84 (M84A-002). I cant find any run switches on it...
Replies
4
Views
2,496
I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
Replies
2
Views
177
Hello, I have some Modicon 884 files that I need printed out. I would rather not buy a whole software package, all I need is the print out of a...
Replies
4
Views
1,883
Hi I have a Modicon Quantum 540 14A CPU that evertime I cycle power to it, it seems to lose the software (at least thats what the Modicon tech...
Replies
1
Views
2,160
Dear All, i have redundant quantom from modicon. -The application program was worked very good ,Before,i changed the resolution of RTD module to...
Replies
0
Views
1,797
Back
Top Bottom