Allen Bradley 1100, no communication, error 187h

go to your control panel, network settings,local connection status, find IPv4, properties,
Check box "use the following IP address"
and put in 192.168.210.xxx (anything different from your micrologix) use subnet 255.255.255.0
and try to re ping it
 
In two pics you show an ethernet device driver and one ethernet/IP. You want ethernet/IP. I would try using bootp to static the IP address on the controller if you cannot do it from the advanced settings on the face.
 
Something else silly to check is the program mode/run/remote. Also hardware config should not keep you from getting online and uploading program from the PLC there is even a box you can click to ignore missing modules and run. Unfortunately I do not have 500 installed at the moment to be more detailed.
 
If he is unable to "ping" the processors IP it will never show up in RS Linx
I also use Ethernet Device in RSLinx as my driver
 
go to your control panel, network settings,local connection status, find IPv4, properties,
Check box "use the following IP address"
and put in 192.168.210.xxx (anything different from your micrologix) use subnet 255.255.255.0
and try to re ping it

Sorry for the delay, I eventually find it, ping works I believe thank you

FSC5.png
 
Last edited:
I believe I have achieve communication, thank you everyone and props to roxusa, never in any other tech forum have I fix a problem as fast.

There is an old program there, I will now try to make my own and make a new thread if needed. I just need to send data to the plc, turn on some
lights and maybe receive a sensor reading.


I just put clear error from the pc and the blinking led stop.

FSC6.png
 
Last edited:
I always like to use "go to error" instead of "clear fault" to confirm what the fault is on a processor
 

Similar Topics

Hi All, I am working on an application where I must use EIP communication to a ML1100. (Not enough IO). I have the Camera writing the Pass/Fail...
Replies
15
Views
6,460
Good afternoon. I need help on how to communicate the HMI KTP400 siemenes (using TIA Portal V12) with a MicroLogix 1100 Series B using RSLogix500...
Replies
0
Views
1,562
Hi, Everyone :site: I am a beginner to PLC. Recently, I am working on a project to build a door cycle tester utilizing Allen Bradley (1100) and a...
Replies
3
Views
2,091
I was told to purchase a CBLGEN01 cable and CBLADK03 kadet adaptor to connect my AB 1100 to a Redlion G304K HMI. This info was given to me by Red...
Replies
14
Views
6,437
I am wondering if anyone had success connecting AB 1100 to a Red lion C304K. My problem is that I am having a hard time understanding I/O to tags...
Replies
8
Views
3,636
Back
Top Bottom